Hi,
I would like to setup two Compactlogix PLCs so if one fails the control of the I/O will failover to the second PLC. The application can handle the a non bumpless transfer.
I have 2 compact logixL30ER, a Stratix 1783-EMS08T/B Switch and a 1747-AENTR connected to an I/O rack with SLC I/O
In the logic I state that if one CPU runmode is not running I inhibit the connection, and the second PLC will be given ownership of the I/O rack.
I see a fault on the I/O Rack and switch connection properties.
Code 16#0106 / Module owned and configured by another controller
It seems that it does not fully release the connection from the CPU that originally was connected.
Is there a way to fully release force the connection to close?
Thanks
I would like to setup two Compactlogix PLCs so if one fails the control of the I/O will failover to the second PLC. The application can handle the a non bumpless transfer.
I have 2 compact logixL30ER, a Stratix 1783-EMS08T/B Switch and a 1747-AENTR connected to an I/O rack with SLC I/O
In the logic I state that if one CPU runmode is not running I inhibit the connection, and the second PLC will be given ownership of the I/O rack.
I see a fault on the I/O Rack and switch connection properties.
Code 16#0106 / Module owned and configured by another controller
It seems that it does not fully release the connection from the CPU that originally was connected.
Is there a way to fully release force the connection to close?
Thanks