Error 84h Micrologix 1200

Join Date
Nov 2004
Posts
4
HELP!!!

I have a Micrologix 1200 that keeps faulting out. It displays Major Error Code 84h and the description says "The maximum number of expansion I/O power supplies allowed was exceeded." What does this mean??? There is only one power supply and it is located in the processor. I do have an external supply for the AIC+ but that shouldn't affect the processor should it? This happened once before I even had the AIC+. Like I said, what does this mean and how do I correct it? Any help is greatly appreciated.
 
ML1200 can support up to 6 expansion modules, depending on type .
Sounds like the combiantion you are using exceeds the maximum power consumption specification.

Use this LINK for the user's manual, Appendix F has a worksheet to determine system loading.
 
Last edited:
I think I have it narrowed down. I disconnected all the expansion I/O and started hooking it back up one slot at a time. The analog module faulted the processor with the same error code. I am going to try to find a dedicated control and eliminate the analog all together. Thanks for all the feedback!!!
 

Similar Topics

Hello Everyone, I have a issue with communication between two different PLCs. So here is the facts, The Master PLC is Guard Logix 5069 with IP...
Replies
4
Views
80
Hi Siemens guys! I am experiencing SF fault on our S7-300 (6ES7 315-2AH14-0AB0) CPU from time to time. I've checked the diagnostic buffer and...
Replies
13
Views
170
Hello..I am new to Plc.I have Mitsubishi Melsec Fx3Ga-40MR PLC controlling a machine for packing powder.Currently the Plc has issue which power...
Replies
3
Views
139
hello, I'm a student and for my final grade I have to repare a sepro robot. the only problem I have for now is that i have an error code 3...
Replies
0
Views
35
Dear All, i am trying to connect Danfoss inverter with s7 200 cpu 226.but microwin shows following error at DATA Ptr.i assigned different VB...
Replies
1
Views
46
Back
Top Bottom