Error 84h Micrologix 1200

Join Date
Nov 2004
Posts
4
HELP!!!

I have a Micrologix 1200 that keeps faulting out. It displays Major Error Code 84h and the description says "The maximum number of expansion I/O power supplies allowed was exceeded." What does this mean??? There is only one power supply and it is located in the processor. I do have an external supply for the AIC+ but that shouldn't affect the processor should it? This happened once before I even had the AIC+. Like I said, what does this mean and how do I correct it? Any help is greatly appreciated.
 
ML1200 can support up to 6 expansion modules, depending on type .
Sounds like the combiantion you are using exceeds the maximum power consumption specification.

Use this LINK for the user's manual, Appendix F has a worksheet to determine system loading.
 
Last edited:
I think I have it narrowed down. I disconnected all the expansion I/O and started hooking it back up one slot at a time. The analog module faulted the processor with the same error code. I am going to try to find a dedicated control and eliminate the analog all together. Thanks for all the feedback!!!
 

Similar Topics

I am kind of new to GE products, but we have several in my area. I made a minor logic change and it verified good, but when I tried to download I...
Replies
5
Views
45
Hi, I'm currently having issued with a PowerFlex 252. It was working fine last week, and suddenly decided to stop working. When I go into...
Replies
2
Views
120
Hi there, I'm new to plc programming and was wondering why I get this error code when I run my simulation for these temperature sensors? What I'm...
Replies
2
Views
90
Hi Everyone. Not posted on here for a long time, but I am hoping someone can help me. I am doing a differential pressure calculation in a L27ERM...
Replies
16
Views
425
Hello Everyone, I have a issue with communication between two different PLCs. So here is the facts, The Master PLC is Guard Logix 5069 with IP...
Replies
4
Views
131
Back
Top Bottom