Hello
We are trying to setup a PV plus 1250 running on RIO,
we can't seem to locate where to change its station address number... Any ideas?
George
 
1000 words

In Communication setup, add the remote I/O adapter for the PV+

Right Click on the RIO Data and select Configure I/O

In the RIO Configuration window, select Add Rack.

In the popup, the Rack # buttons appear greyed out. They're not.

But once the Rack has been made, you won't be able to change it. You have to delete it and add the new one.

[attachment]

Mind you - I've never done an RIO PVP, so this is all theoretical.

plcs.net.jpg
 
Last edited:
hi, in FactoryTalk view ME v5,

the scanner there only have 1747-SN,
but I'm using 1747-BSN, which one should I select ?


I try to select 1747-SN series B or A but the
panelview plus 1000 RIO link is fail.

Please help.

Thank you.

bsnRIO.jpg
 
help me communicate a PanelView Plus 100 with a PLC 5/80 "RIO"

Hello, If anyone can help me communicate a PanelView Plus 100 with a PLC 5/80 "RIO", the forum helped me not much ... I would appreciate please. But I can not speak English translation online.
 

Similar Topics

Hey guys, I'm at a bit of a loss with a problem I'm having with some PVP 1250s and hoping for some advice. In firmware and application version...
Replies
0
Views
290
is it possible to comunicate a powerflex 753 (ccw) using ethernet 20-750-ENETR card to a panelview plus 6 1250 (factorytalk view studio me)...
Replies
0
Views
1,494
Hello, I recently installed an **** Flexy 201 so we could monitor our PLCs (one SLC 500 and one Control Logix) remotely under a VPN. One of the...
Replies
0
Views
2,348
Hi, I have a customer that has an intermittant issue with a PV+ (2711P-T12C6D1) and they would like to replace the PV+ with the latest PV+7...
Replies
3
Views
2,984
I have these PLC and HMI and want to communicate them. I made a program in RSLogix5000 and FactoryTalkViewStudio, tried them out with FT station...
Replies
7
Views
4,410
Back
Top Bottom