2 Frequency Drives and 2 AC motors

userxyz

Member
Join Date
May 2002
Location
any
Posts
2,768
Hi,

I connected 2 AC motors (mechanical); 1 motor must have a Torque limit. The max frequency difference is 3Hz.

On motor turns at 50Hz and the second at 53Hz. The one that turns at 50Hz has the Torque limitation.

The drives are 2 MM440's from Siemens.

How much Nm can I set ?
 
I have to make some assumptions on your application but try this.

Use a single 0-10vdc speed input signal to both drives. In the drive parameters, set your min and max speeds including whatever speed difference you want. For example, it sounds like the max speeds would be 50hz for one and 53hz for the other. If you want minimum speed to be, say 20hz, set 23hz for the drive with 53hz and 20hz for the drive with 50hz. That way you will always have about 3hz offset in the motor speeds.

To get a current limit, find the drive parameter for current limit and set it for whatever level you desire. Better yet, it the drive has a torque limit setting use that instead. It's a little more accurate.

As for available torque, you need to figure that from the motor nameplate speed and kw. The formula is Torque (Nm) = kw/rpm times a constant. I don't know what the constant is in the metric system. Someone help us out on this, please. I spend my time in the world of ft-lbs and hp where the constant is 5250.

Hope this gets you going
 
Did some quickie unit conversions and it looks to me like the constant is still 5250 for the metric units. Someone please check me on this, however.
 
DickDV said:
Did some quickie unit conversions and it looks to me like the constant is still 5250 for the metric units. Someone please check me on this, however.

Dick

Using your formula, I substituted the following values in.. 1Hp and 100rpm and came up with 52.5ft-lb (nice easy values to work with)

I then redone the calculation using 0.746Kw and 100rpm and came up with 39.165Nm. (I have taken 1Hp as 746w)

1Nm is 0.738ft-lb so 39.165/0.738 = 53.07ft-lb.

Paul
 
I am putting this up with the other one. Formulas for these calculations can be obtained at: http://www.patchn.com/motorformula.htm

I have a question. Did the original post mean he had mechanically connected 2 motors?
IF SO
What application would you mechanically connect 2 motors then run them at different speeds?
 

Similar Topics

I need to collect data (yet to be specified, but voltage etc) from a bunch of VFDs (Powerflex 753) connected to Allen Bradley (ControlLogix) PLCs...
Replies
16
Views
4,272
Good Morning , I just installed some 1 hp Lenze AC Tech 480 Volt Drives. I have seen this with other drives also. I went with a 8 Amp B Curve...
Replies
8
Views
3,873
Good Morning , We have a few 125 HP motors that have Soft Starts on them and I would like to replace them with VFD's. What energy cost...
Replies
7
Views
3,252
I've seen VFDs protected with all of the following... Is there any standard dictating what type of device a a VFD should be protected with in the...
Replies
1
Views
2,100
How to make addressing for VFD via modbus to plc and HMI scada?
Replies
1
Views
2,198
Back
Top Bottom