I have an application where I am using a SST-PFB-SLC in slot 2 of a SLC500 rack. The SST-PFB-SLC is connected to a profibus panelview. This aspect of the project works fine. Now I am required to insert a new machine into this network. This machine will use a SST-PFB-SLC to communicate with its own profibus panelview. I need to exchange data between the two SST-PFB_SLC's. Any advice how to transfer data? Should one be configured as a slave the other a master?

Thank you for your advice,
Derick
 
You will probably have to add an additional SST-PFB-SLC module to each rack, if the existing modules are already communicating with PanelViews (the second port on the PFB modules is for config. only). What type of SLC processor are you using? You may be better off setting the two CPU's up on their own DH+/DH-485/Ethernet network.
 
Another option is to use a Siemens PD/DP coupler to transfer data between two masters. PN is 6ES7 158-0AD00-0XA0. This unit has two Profibus ports. One for each network.
 
Thank you AJZ and mgvol for taking the time to reply, I appreciate the benefit of this site and the technical skills of it's members. In response to your question mgvol I am using an SLC 504 1747-L542 (32K) processor in each rack. I see that your suggesting I look into DH+, DH485 or ethernet. I am preparing to do this as an alternate if I am not sucessful. I was wondering is it possible to use multiplexing addresses to send data between the two SST-PFB-SLC in each rack since both are connected to panlviews and using real time addressing?

thanks
 
Well, I'm afraid you're way beyond my level of experience with the SST-PFB-SLC product; I can set one up w/Hyper Terminal and RSLogix 500 and that's about it. However, since you are using 5/04 CPU's, why not just connect a piece of "blue-hose" between Channel 1 of the CPU's and use MSG instructions to send/receive data? Probably the least complicated, least expensive route to go.
 

Similar Topics

i am looking for a profibus scanner SST-PFB-SLC Version 1.0 for SLC 5/03, but it's hard to find. I see the same model number, but version 2.0 on...
Replies
2
Views
2,492
Hi All, I have siemens CPU-300 with DP port. which i am using as master for DP slave. Now i had some SLC IO which i want to connect to the same...
Replies
2
Views
4,774
hey guys i would like to say this is the best place i have found for plc ???? so this is where i come for my ? i have a sst-pfb-slc card. the...
Replies
1
Views
3,287
In a 1756 Controllogix(CLX) chassis there is a SST Profibus module, i have the configuration Software for CLX but do not know or have the...
Replies
3
Views
6,766
I have 2 SST-PFB-CLX modules (Slot3 and Slot6) in my 1756 A/B PLC. Both modules are working O.K. I tried to upload actual configuration using SST...