sst-pfb-slc card

pdelno

Lifetime Supporting Member
Join Date
May 2004
Posts
79
hey guys i would like to say this is the best place i have found for plc ????

so this is where i come for my ?
i have a sst-pfb-slc card. the problem i have is i have no config file for this card and the componey that mad the piece of equiptment is out of busness and i fear the day we lose this card.
the card conects 2 seimans drives to a slc 500 is there a way to get the config out of he card to back it up or will i have to fumble my was and make a new config file
 
The module should have an RS-232 serial port on it, which you can connect to SST's Profibus configuration software utility. This should allow you to upload the configuration from the module. I think that utility is free from www.MySST.com.

I think that recent SST-PFB-SLC modules were even compatible with Siemens' own COM PROFIBUS software, so that could recover the configuration too.
 

Similar Topics

i am looking for a profibus scanner SST-PFB-SLC Version 1.0 for SLC 5/03, but it's hard to find. I see the same model number, but version 2.0 on...
Replies
2
Views
2,497
Hi All, I have siemens CPU-300 with DP port. which i am using as master for DP slave. Now i had some SLC IO which i want to connect to the same...
Replies
2
Views
4,779
In a 1756 Controllogix(CLX) chassis there is a SST Profibus module, i have the configuration Software for CLX but do not know or have the...
Replies
3
Views
6,788
I have 2 SST-PFB-CLX modules (Slot3 and Slot6) in my 1756 A/B PLC. Both modules are working O.K. I tried to upload actual configuration using SST...
Replies
0
Views
1,731
I need to set up some messaging between an old Simatic TI 545 PLC (part number is 545-1104) and a ControlLogix L55. I have an SST-PFB-CLX module...
Replies
2
Views
10,006
Back
Top Bottom