just wondering whats the diffrence in the current out puts of the powersupplies, i have a s7 cpu-300 PLC with DI/O and AI/O moduals, is it better to get a PSU of 5A or 20A, whats better and why are there diffrent out puts, thanks
 
To answer your question, go to the module specification sheets (in the catalogue or on the net) and do a power budget for your projected configuration. Then choose a power supply that covers the requirements.
Hope this helps,
Daniel Chartier
 
Hello;
Power budget means summing Amps needed on the 24 V backplane + Amps needed on the L+ supply of the modules (if they are fed from the same power supply). Here are some extracts from data sheets for different S7-300 modules:
Power_budget.jpg

Simply look up the data for each module on your rack and add the different values. Keep a safety margin in case of short-circuit (I feel confortable with 50% spare power).
Hope this helps,
Daniel Chartier
 
hello,

im not quite sure how to do it, but i took a stab and i think i got about 10A would be ideal, can you check for me the power budget, this is what i have:

1 X Siemens S7 314IF PLC #6ES7 314-5AE02-0AB0

3 X Siemens Digital Input/Output DI16/DO16xDC24V #6ES7 323-1BL00-0AA0

1 X Siemens Analog Input AI 8x12bit #6ES7 331-7KF01-0AB0

1 X Siemens Digital Input DI16xDC24V #6ES7 321-1BH01-0AA0

thanls in advanced
 
to add on that, i have a 5A powersupply, is this suffeince for the above list. thanks
 
Hey, why not ask Siemens to do the arithmetic for you? If they're going to sell you (or have already sold you) a PSU, the least they could do is give you some indication of whether it will work or not. Give them a ring and see what they say.


Ken
 

Similar Topics

I am troubleshooting an actuator which is not responding to the plc code. The range in the channel of the Allen Bradley 1756-OF8 Analog card is...
Replies
1
Views
637
Hi, I work in a brewery in North Carolina and I need some help finding the output current for a VFD in the PLC. First off I am new to working with...
Replies
5
Views
1,383
I do not work in the AllenBradley field much, but we ran into an incident that I thought was unusual. Its a 480V vfd. The input current is 59.6...
Replies
20
Views
8,550
I have been trying to find a way to get the Output Current from some PowerFlex drives to read to my ControlLogix plc. These are all running off of...
Replies
2
Views
1,464
Hi all. Will something like this work on a VFD output ? Carlo Gavazzi E83-2050 The VFD output frequency will be between 45-55 Hz. I know that its...
Replies
6
Views
2,185
Back
Top Bottom