There is a lot of choices for doing controlling I/O remotely. Here is what I have.

I need to go from a SLC 5/03 to a remote location about a distance of 400' to 10 digital inputs and 10 digital outputs at 24v.
I am looking for the least expensive set-up. I have device net software but there is already a 2 conductor shielded cable ran that can be used for remote I/O. Please recommend a set-up I should use.
I am thinking of using a 1747-SN RIO scnaner to a 1791 Standard block I/O. Let me know what you think.
Thanks
 
The least costly method of doing this is probably with the remote I/O scanner. Since you already have the cable installed, why not use it and avoid the cost of further installation. If the block I/O used in remote will do the job, sounds like a winner to me. You should consult your local AB distributor on matters of cost and also any late breaking equipment that you may not be aware of. I try to get by the AB site pretty regularly but am continually amazed at how quickly things seem to change. Hope this helps.
Randy L.
 
As long as the twinaxial cable is really suitable for Remote I/O, that's definitely the simplest method.

The I/O should be fairly inexpensive, too; A-B just released "CompactBlock" I/O with a RIO adapter built in. You could get the 16-point DC Input block with the RIO adapter and get a regular 16-point DC Output expansion block to fill your I/O needs.

http://www.ab.com/io/1791dnew.html
 

Similar Topics

Hi, We have been facing a issue with SCADAPack 474. Configuration is like below. RTU 474 + 6103 PS + 5606 IO Mix Module + 5414 DI Module Only...
Replies
0
Views
62
Hello, Can anyone recommend an expandible IO module with OPC UA? I've deployed the Emerson RSTIO-OM module and it works great, but it has a...
Replies
0
Views
52
So I'm pretty new around here but I come looking for advice or suggestions to research. Im the plant electrician/SCADA guy for a warer department...
Replies
8
Views
269
See the screenshot of EIP tag list. We are trying to read in a digital input that is hard-wired. It is shown here as I31.1. I believe we cannot...
Replies
7
Views
302
Hello Dear users, I am writing about a problem that has been bothering me for a few days, i.e. I am trying to establish remote access to the Allen...
Replies
0
Views
103
Back
Top Bottom