I am currently quoting on a job. CompactLogix with 10 pumps and drives. The profibus card from SST is around $2500 and 2 analog inputs (IF8) and outputs (OF8C) are roughly the same price.

I will have some learning curve if I go with the SST card and none using straight I/O although I have used the SST Cards for profibus encoders in the past.

I checked on the pumps and drives and they both support DP so no couplers needed.

Other than wiring, can anyone think of a good reason to go with the profibus card vrs. traditional analog modules.
 
No errors on the signal. We had frequency inverters on analog signals from the plc. (0-10VDC). Even though the analog output of the plc is constant, the signal fluctuats a tiny bit. (5.1V instead of 5.0VDC for example). With profibus there are no such errors. If you start using profibus, make sure you get some information about maximum cable lengths en bitrates. 12Mbit/s is not possible over longer distances. Also for high bit rates (3Mbit/s-12Mbit/s) you need a minimum cable length of 1 meter. (Has something to with signal reflections on the bus).
 
Suggestion: Use analogue as the primary solution on all ten drives, but provide Profibus (as well) on one drive. If you get the time, you can "learn" the profibus system but at almost no risk to your project. OK you have to buy a Profibus card but you may be able "borrow" one from your supplier if he is keen to promote this type of solution.
 
Profibus

I think most new installation are moving to bussystems as a IO network with your discrete IO wired to a remote profibus node, alot of newly launched equipment cater for the profibus protocol, Ease of installation ,Ease Diagnostics, Faultfinding. No more messy wires in Control cabinets.

I love the idea, and where possible only use profibus with remote IO-->Profibus in the field and profibus on the drives.

Rheinhardt
 
Using profibus will allow you to collect more data just not the drive 4-20 ma and this is an advantage. If you decide to make a modification to your system , for example to see if the drive is tripped , using i/o u will have some complications while using profibus it will be easier
 
If I may humbly suggest, you're going to get a much shallower learning curve, lower cost, and much better functionality using DeviceNet with CompactLogix than you will using Profibus with the same platform, just because the scanning and messaging are native to the controller instead of grafted on through a third party module.

If you can get those drives and pumps with DeviceNet, you're going to have a much easier time with this project.
 
Everyone has given me a lot to think about. I had just about made up my mind about Profibus till Ken's post about DH+. The meters are Endress+Hauser ProMass 83.

I see where it can save some wiring. On the drive, instead of having to wire a drive fault to a physical input, you could just read it over the profibus.

Ken, the processor is the CompactLogix L35E, not sure about DH+ that away.
 
Confusion reigns

Maybe I'm not getting enough sleep.

You didn't say anything about flowmeters. I didn't say anything about DH+. :unsure:

You might have to restate your system architecture before any experience or advice can be applied.
 
You are right Ken, I did misread your answer, did you ever read something and your brain saw it another way. (DeviceNet not DH+) I have found out a little more info on the meters since my first post. I have also did some research on the E&H profibus meters.

I also came across some articles about companies replacing their old meters and such with Profibus that was very educating.

Sleep now, reclaim brain cells.
 
Using a network will simplify wiring. Watch the terminators. Only 1 needs to be on. You will most likely be able to change drive parameters from the master PLC. Profi bus need a continuous ground/shield connected on both ends and at every node to work right. With a networked sysetem you can connect at one point and monitor the TOTAL system. Yeah the up front cost is higher, but the long term benefits are worth the cost.

Then when the customer gets additional systems, the ability to network the plant is easier. BTW, you can network various mfgr's and networks on ONE system so I have been told.
 
you're going to get a much shallower learning curve, lower cost, and much better functionality using DeviceNet
A lot cheaper too and certainly does the job.

I use Device Net wherever I can quite frankly.
 

Similar Topics

Hi, I was noticing that Profibus connectors have 2 ports on them that can house 2 separate cables. Can I use 2 cables with Profibus signals...
Replies
4
Views
176
Hello, I am in possession of a WAGO PFC 200 750-8216 which I was successfully able to set up as a Modbus RTU Master to a slave device using...
Replies
0
Views
79
I am trying to implement a profibus network and am a newbie in the automation and communication industry. what are the components required for the...
Replies
1
Views
103
Hi, I am using TIA Portal V18. I have imported a (v5.7) SIMATIC manager project via device proxy. I have created a HMI project (TP700) in TIA...
Replies
2
Views
319
Hi Folks, I am new to the S7-300 and the whole Profibus communication. And I just wonder that can you connect a S7-300 module to a Beckhoff Bus...
Replies
1
Views
318
Back
Top Bottom