I have to add some I/O cards to a ControlLogix PLC.
Here's the configuration:
1st chassis - 17 slot with CNB card (no spare slots)
2nd chassis - 17 slot with CNB card (1 spare slot)
3rd chassis - 7 slot with CNB card (6 spare slots)
I need to add the cards in the third chassis and somehow re-schedule the ControlNet network. Is it possible to do this without a 1784-PCC? Tho only comms options are DH+ (via DHRIO card in the 1st chassis) or DF1 (via the processor serial port).
I've done a search on this forum and found a post from a couple of years ago which suggests it may be possible to re-schedule the network using DF1 passthru to the ControNet network, but I,m not totally convinced. The CNB manual suggests that Ethernet or 1784-PCC is the only way.
Whilst on site yesterday, I attempted to gain access to the ControlNet network using DF1 and RSNetworx for ControlNet, but I was unsuccessful (error message "cannot find the active keeper ..." The PLC was in run mode - does it need to be stopped?
Any help is appreciated as I really don't want to spend hundreds of pounds for a 1784-PCC just for this.
I have to add some I/O cards to a ControlLogix PLC.
Here's the configuration:
1st chassis - 17 slot with CNB card (no spare slots)
2nd chassis - 17 slot with CNB card (1 spare slot)
3rd chassis - 7 slot with CNB card (6 spare slots)
I need to add the cards in the third chassis and somehow re-schedule the ControlNet network. Is it possible to do this without a 1784-PCC? Tho only comms options are DH+ (via DHRIO card in the 1st chassis) or DF1 (via the processor serial port).
I've done a search on this forum and found a post from a couple of years ago which suggests it may be possible to re-schedule the network using DF1 passthru to the ControNet network, but I,m not totally convinced. The CNB manual suggests that Ethernet or 1784-PCC is the only way.
Whilst on site yesterday, I attempted to gain access to the ControlNet network using DF1 and RSNetworx for ControlNet, but I was unsuccessful (error message "cannot find the active keeper ..." The PLC was in run mode - does it need to be stopped?
Any help is appreciated as I really don't want to spend hundreds of pounds for a 1784-PCC just for this.