Versa Max - Faulted

teh

Supporting Member
Join Date
Nov 2002
Posts
140
Hi All,

I have problem with Versa Max Micro IC200UDR005 - AA,

when i attached the expansion module , IC200UEX636-B(4AI/2AO)

and download the hardware configuration file to the CPU. the

following warning message " system configuration mismatch "

come up in the fault table. and the CPU cannot put in run mode...

why?? i have try and try many many times..

please advise..

regards
 
The fault message means that there is a discrepancy between the configuration file you downloaded to the PLC and the actual hardware physically present.

You need to correct the discrepancy and then clear the fault table before you will be able to start the PLC. Note that the entry into the fault table will not go away automatically when you correct it. You must open the PLC fault table with the programming software and clear it.
 
Dear Mr. SteveI coun't find out the reason of system configuration mismatch..
I had checking all around the hardware configuration but i still
fail.. the " system configuration mismatch " still appear when i was download the data to PLC..

Is it the version of my CPU ? ( IC200UDR005 - AA ) and the Analog
module what i used is IC200UEX636-B..

I totally have no idea on it.

Regards
 
TQ..

is it will cause analog In/Out out of function?
I measured by measurement equipment on %AO00013 but was no mA output..

regards
 
The file you posted doesn't match your description.

Your file shows a 28-point base unit with two analog expansion modules in positions 1 and 2 plus a discrete expansion module in position 3. Is this what you actually have connected?
 
Yup it is what i actual connected,
any where we have solve the problem..
Is because of the version of the CPU IC200UDR005 - AA.

"AA" is the Very old version of this model..

I try to used IC200UDR005 - BB now anything look OK..

Is any solution to solve my AA CPU?.. Something like

Download some software to MicroChip of CPU..

( I know that directsoft can do it ).

Any where Thanks you for support!:cool:

Regards
 

Similar Topics

Hi, I am looking for some help with a GE Fanuc Versa Max Micro Controller model IC200UDR001-BF connected to a Quickpanel mini display...
Replies
3
Views
145
I am new to this forum and tried posting a question earlier but did not se it in your listing. I have been trying to print report for a Versa Max...
Replies
3
Views
1,451
Can any body please tell me what is the software required to communicate with Ge-Fanuc Versamax IC200UDD110-BF
Replies
3
Views
1,443
Hi Im trying to fire modbus RTU command (read coils 02) when im processing the commreq im getting status word value 524.Im using PLC...
Replies
0
Views
1,778
I'm using versa max micro controller in model IC200URD64/164. Just encounter this problem. Usually i'm use Proficy Machine Edition to program it...
Replies
7
Views
2,738
Back
Top Bottom