AD GS1 Drive Problems

zmanvortex

Member
Join Date
Apr 2002
Location
Nebraska
Posts
216
We are using an AutomationDirect GS1-10P5 1/2hp drive that takes 120vac input and outputs 230vac 3ph. We have one customer that says the drive had sparks and smoke come out of it when they powered it up. We had their electrician check all the voltages which checked out ok. We sent them another drive and the same thing happened to it when they applied power to the machine. I called AD support and here is what they told me.

"On our GS1 1/2hp models there is the possibility of a 150A inrush current while charging the dc bus, if there is a good capacitance transformer supplying the power to the drive. After repeated high current charging the drive can possibly fail. Our new GS2 120vac in 3ph out models have a soft charge feature which eliminates this possibility."


Has anyone else had this problem?
 

Similar Topics

Hi, I'm trying to send write (MWX) commands from DL06 for frequency and start/stop control of a motor connected to a GS1 Drive. The GS1 Drive...
Replies
1
Views
1,528
Hi Friends Here in a new project, I'll need to control a GS1 drive from Automation Direct using a Master K120S PLC MODBUS connection, is it...
Replies
0
Views
1,751
Does anyone know what cable you use for this and since it takes up Port 2 how could you run a Display also. I saw the FA-ISOCON but how does that...
Replies
7
Views
3,089
I asked this question over at the A-D forum, but the response time 'round here is much better... :cool: When using the front panel potentiometer...
Replies
9
Views
5,451
I have a scanner that reads barcode GS1-128. The reading is presented in a SIMATIC S7 PLC as one long string in a DB (DB15 in example). I need to...
Replies
11
Views
5,147
Back
Top Bottom