I'm trying to send write (MWX) commands from DL06 for frequency and start/stop control of a motor connected to a GS1 Drive.
The GS1 Drive is communicating fine with SP116 turning on every time the PLC tries to communicate with the GS1 drive and counter shows the no of successful connection attempts were made. The SP 117 never turns on, so that means there is no unsuccessful attempt at communication.
I' using a simple rung with a normally open contact to trigger an MWX Block. However, when I try to send the write commands for frequency value or start/stop of a motor connected to the GS1 drive, it doesn't go through.
The settings on secondary comm port of plc (port2) and the mwx settings exactly match the gs1 drive settings. I'm not sure whats wrong.
MWX Settings for frequency control of gs1:
CPU
K0
port no: k2
slave addres: k1
Function Code: 06
Start Slave memory Address: K42331 ,
Start master memory address: V3000,
Modbus Data type: 584/984 mode
Secondary comm port:
Port2,
Modbus,
Baud Rate 9600,
Station No: 1
Stop bits: 1
Parity: odd
Gs1 Drive settings:
P3.00: 04
P4.00: 05
P9.00: 1
P9.01: 01
P9.02: 05
Also I am able to control the motor with the drive alone and I have the electronic chip relay disabled on the drive (not sure if that makes any difference).
I would really appreciate if somebody could help me out with this.
Hello, I need to restore runtime application in Application Manager (Rockwell) and I have a problem during I restore runtime. Application Manager...
1,363
Hello Members, I hope you are all doing well. Coming back to my issue , I had recently converted an backup which was mae for FTV 8.10 to the FTV...
1,589
Hello everyone, I am currently working on a project for Factory talk view 6.10 SE. When I open the program, there are several error messages...
23,004
I am unable to control an Danfoss inverter VLT 2800 via profibus using Siemens S7300 PLC. Communication between PLC & VLT 2800 is established...
4,057
I am running CCW 13 trying to upload to a micro 820 vers.12 I get an output message OPC server is unable to load project controller. Please help!
263