Simple answer is "No," but you can create a 1st scan bit. This would be for S7-300/400. (Haven't used S7-200 in a few years and it used to be programmed by S7-MicroWin, not Simatic Manager and was a little different).
Depending on CPU, you have 3 OBs that run at startup; Cold, Warm and Hot.
The main difference is if you restart the CPU by going from program to run or cycle the power.
In the past I have SET a bit in the start up blocks and then after a 2-second delay in another block (FC or OB1) RESET the same bit. This gave a pulse to the SCADA system to tell it the PLC was starting up.
Any questions, please ask.
SMY