I am trying to connect a TP170A to a CPU315-2DP. I have connected it to the MPI port and it works ok but I prefer to use the second port which is DP. Are there any setting in the Hardware setup of the CPU which I have to make?
 
Geofra,

You will need to enable the DP port on the 315, you do this in Netpro, just set the DP port as networked, compile the new configuration and downlad it to the PLC.

Paul
 
Tp170

Thank you for the answer , but who is the master and who is the slave? Do I have to give a different address to the DP port than the CPUs address?
 
CPU and TP definitely have to have unique addresses.
Default are 0 for the PG/PC, 1 for the OP/HMI and 2 for the PLC. You may want to assign different addresses than the default.
Both PLC CPU and TP can be masters on the bus. For most applications this is the normal actually.
The MPI port and the DP port on the CPU can have the same addresses, or different addresses. There is no dependency between the two.

edit:
If you are using the Profibus port for i/o as well as the TP panel, then I recommend that you make the whole thing as an integrated project.
This because the "Target Rotation Time" has to be calculated (by STEP7), and STEP7 then need to know all the stations on the network.
(You can manipulate STEP7 to take the TP into account, even without an integrated project, but it takes a few more steps).
 
Last edited:

Similar Topics

Hi guys, I have Siemens TP170A with touch non-operative. I have replacement but Touch Screen do not work (cannot set Transfer Mode to make a...
Replies
9
Views
2,343
I have a siemens tp170a hmi and tried just for fun, to use modicon modbus driver settings and communicate with a regin roomcontroler. I use the...
Replies
2
Views
2,126
I am trying to extract an existing program from a Siemens TP170A HMI, using ProTool CS. Thus far, I have been unable to establish communication...
Replies
7
Views
3,442
Hello, Is it possible to upload a project from a TP170A panel to a PC? The "backtransfer" option is not active for this panel in the WinCC Flex...
Replies
1
Views
2,239
Dear friends, I have SIEMENS Touch Panel TP170A which is connected to S7-200 PLC via PROFI-BUS. While installing new Touch screen, it is not...
Replies
4
Views
8,424
Back
Top Bottom