Regarding allen bradley slc plcs. What is the differance between the keyswitch being in rem. vrs. run??
Thanks in advance for any replies!
 
If it's in RUN, you can't switch it to program mode via RSLogix. In REM, you can change between remote program and run modes through software like RSLogix.
 
With the key in the run position, you cannot place the processor in program mode via software. With the key in the rem (remote) position you can change the status of the processor to run or program mode via software. Also if the key is in the program position, you cannot place the processor in run mode via software.

The 5/01 and 5/02 do not have a key switch, so are always in remote mode.
 
Thanks guys!! I knew it was something like that!
icon7.gif
 
and a little bit more ...

plus ... while in the RUN position, you can NOT make edits to the program rungs ... for example: you cannot change the address assigned to an XIC, etc. ... but you can still change the values located in variable locations ... for example: you can change the Preset of a timer ...

while in the REMote RUN position, you CAN make edits to the program rungs - by going through the Edit/Accept/Test/Assemble steps ...

plus you can NOT do a program download while in the RUN position ... the keyswitch must be changed to REM or PROG before you can download ...
 

Similar Topics

I am developing a modification for our production lines for OEE, when the line stops i move the current Date/Time to my DB and when the line...
Replies
8
Views
2,312
See picture. I want to add a rung (magenta) into the existing code. Can't figure out how to do this. I select a -||- , right? When I drag/drop...
Replies
21
Views
1,879
Hi All, On my site, the standard template for storing recipes in the PLC is to create a tag called PartRecipe which is an 2D array - for example...
Replies
4
Views
1,497
I would like to do change a kinetix drive, so i believe i just have to put the IP address in the new kinetix and just connect right? Do I need to...
Replies
1
Views
1,213
Hey all, I am trying to check in logix designer in emulator and I need to check the hmi alarms by toggling bits to activate an alarm . But...
Replies
4
Views
2,083
Back
Top Bottom