How far realisticly can i run a 4-20mA signal ?

I am looking at about 150 meters back to an NI16I card.....
 
I n theory you could run this farr as the moon. It all depends on the cct resistance.

The bigger the cable, the farther you'll go.

What to look at is the transmitter. It must be rated for a certain impedance.

150 meters is usually a piece of cake. I have runned this in the thousand of feet.

Say you run the loop on 24 Vdc and at the other end there is a 1-5 volts conversion going on in the input module. You'll need to have enough voltage left after the drop due to the cable lenth, to pull the 1-5 volts.

24 volts / 20 mA = 1.2 Kohm

The total loop resistance must not be over this or the x-mitter will not have the mean to push the signal through it.

What is the cable resistance ??? You must by now realise how far you can push the signal :)

Very farrrrr.
 
many thanks boys

I thought it was the case (resistance wise)!

just wanted to check as all my signals are normally 1-10 meters max, on a project that has 8 x 150 mtr loops and didnt want to make a **** up !
 
Personally Sounds like a good job for devicenet or control net or whatever communications flavor you like. With needing 8 channels of analog it may be cheaper to go that route. (cheaper as overall not just looking at hardware but also installation)

If there is other i/o then that is a real god possibility.

Drewcrew6
 

Similar Topics

Hi all, Well, here I find myself at a former client after I left water treatment trying to help him get the plant back up and running after a...
Replies
2
Views
1,053
Hi All, I have a question about the input wiring on a HMISCU8B5. I am so close to having what I am after yet it seems so far away. I have...
Replies
34
Views
7,186
I need to go from a powered 4-20mA output (i.e. transmitter supplies voltage) to an Allen Bradley HART input card 1756-IF16H. I cannot set input...
Replies
2
Views
2,438
I'm probably going to be called stupid for asking this. I have only ever used 2 wire sensors. we would connect one wire to 24 dc+ and the return...
Replies
41
Views
7,190
Hi all, Yesterday I was setting up a 4-20mA scale for a tank level. The tank has a staff gauge and a pressure sensor, and the scaling printed on...
Replies
7
Views
2,521
Back
Top Bottom