I've been reading the manual (SLC 500 Instruction Set) on
the PID instruction. The manuals directions for setting the
Kc term seem straightforward. However, for the Ti (reset) term
it states: "a rule of thumb is to set the reset time equal to
the natural period measured in the gain calibration" . I don't
know what is meant by "natural period". Is this the time span
between oscillation peaks when the gain is being set up?
 
basic idea:



suppose that you turn off both the Integral and the Derivative action ... suppose that you crank the Proportional action up to a high level ... suppose that you suddenly step the Setpoint from a low level up to a high level ...



the PV will start to oscillate ... the period of oscillation (from peak-to-peak) is often called the system’s “natural period” ...



here’s an example ...



now then ... whether setting the Integral/Reset action to the same “natural period” is a good idea or not is the subject of much debate ...
 
thanks for the explanation, Ron. I'll be finding out if it is
a good idea or not in my case week after next when we are set
up. Peter, I appreciate the controlguru url. I'll check that out
tonight.
 

Similar Topics

How can I test some PID code I have written for a SLC-500 in RSLogix500, without having an actual processor to test on. I have used Emulate500 to...
Replies
3
Views
1,847
Hello, I have a PID block in my program controlling pump speed in order to get a correct Differential pressure. The way I have it set up is the...
Replies
3
Views
1,284
I have a PID in a SLC 500 that does not function as it should. Have deleted it remade it and still have a problem also moved it up and down in the...
Replies
13
Views
2,765
I am new to the SLC 500 platform and am hoping that someone can give me some hints on how to do PID and ramp/soak with the SLC 500 and perhaps...
Replies
11
Views
6,668
Please Help me to make this PID working. I had done PID according to AB manual but it is not working. when I am manully changing the CV at setup...
Replies
6
Views
7,584
Back
Top Bottom