Hello. I am new to Siemens PLC's and are using a Siemens S7 300 CPU314C-2DP plc, and would like to know how to output an analog referance signal from -+10V to a VSD. The output adresses on the analog card are PQW 752 and PQW 754.
Can this be done in LAD?
 
You are using the "Built-in" outputs. They come preconfigured +-10VDC. The easiest way to test the outputs is to "MOVE" a value of 0 to 27648 to PQW752 which should be exactly - 10 to + 10. If you want to scale the analog out, you can use FC106 UNSCALE from the TI_Converting library. Put 100.0 on the Hi_Limit and 0.0 on the Lo_Limit. Put a MD (REAL) on the IN and PQW752 on the OUT. From a VAT you would be able to put the MD (REAL value) value between 0.0 & 100.0 and the output should go - 10 to + 10
 
I think RRobbins has given you a good answer.
However, over the last three years or so, I have only ever used Profibus to load the speed (and other) information directly into the VSD. Since you are using a DP equipped PLC, you may find this an option.
I have worked on a 314C-2DP only once (I generally use either the 315 or 414), but using DP we could control 6 servo drives, directly writing position and speed information to the drive, and receiving diagnostic information along with position and current feedback.
Of course, if you need no more than two VSDs, the direct analog output method is much cheaper, and often easier to diagnose for the average sparkie.
 

Similar Topics

Hi, I'm curious if anyone has made a master sheet or cheat sheet for all allen bradley card's analog inputs/outputs? As much fun as it is to...
Replies
2
Views
1,578
Hi all, Recently a client had an issue with their Hach sc100 and while I got the instrument back up and running, the analog outputs for the two...
Replies
3
Views
1,567
Hello, I am wondering what the best practices are for testing analog 4-20 mA inputs and outputs. I would like to buy or make a 4-20 mA source...
Replies
12
Views
14,114
Hi All!!! It's my first post on this forum so be a patient,please. I'm writing program using RS Logic 5000 and I need have a variable speed...
Replies
19
Views
8,517
Greetings, My company is working on a panel for an OEM and it is the first time we are using the Micro800 family - specifically the Micro850 with...
Replies
7
Views
5,379
Back
Top Bottom