I Haven't Used A Panel View Pv550 Before ,and I Just Added Another Multistate Indicator To A Screen .
The Tag Editor Is Set Up Okay And When I Validate I Get Validation Passed No Errors .
The States Are Set ,o -- Reads A Message , 1 --- Reads A Different
Message , But When This State Is One High The Screen Reads Error !
Any Help Would Be Much Appreciated .
 
Error is usually reserved for every state not listed in the multistate dropdown box. Take a look at your source word value and insure that no other bits in that word are high. (ie with the radix set for decimal. verify the word value is only 0 or 1 not any other number) If somewhere else in your program that integer is manipulated at the bit level, you will get an error.


Marc
 
As Marc correctly said, the "ERROR" state will show up, if your tag's value doesn't match an actual state in the list.

For discretes, that means you can only use a bit, and have it either false (0) or true (1). Are you trying to use a bit, but reading an entire word, which may have other bits set in it?

For complete types (INT/DINT), you must have a state for every possible value of the INT/DINT you are reading.

Another condition that will raise the ERROR state is if the tag cannot be read from the processor.

One way to get a clue, would but to put a simple test numeric display on the screen, using the same tag that you reference in the Multistate indicator, and see what it thinks it should be.
 
is your multistate indicator LBS ?.i think if my memory serves me correctly with the pv550 you have to have one state true at any one time so if you have no states true the "error" state which is the last state on the indicator will be true.

that's just off the top of my head and it is early
 
panel view ,problem fixed but not solved

I still had a problem with my multi state indicator , where the first state ( off ) caused the problem .
I tried the above Idears to my question , and filled in all the
states but this still caused a problem with the " 0 " state .
All the other states worked fine , I checked the program " bits "
in Decimal values in radix but still had no joy these seemed okay .
I decided to change the multistate indicator to a message display
with the same settings and this worked " fine " .
Sorry I took so long to get back ,your Idears were much appriciated
and I have learnt a few more things about panel views .
The Input on this forum is helpfull for us beginners trying to learn more about the PLC's .
cheers people !
 

Similar Topics

I have been working on this for a while now and I can't seem to get it. I was finally able to view the 1500 on the PanelView under the serial...
Replies
1
Views
82
Hi Everyone, Currently we have three plants running with Controllogix PLCs (L72, L73, L74). In each of these plants we have 2 FTView SE...
Replies
0
Views
55
Hey all, i have a panelview screen (image attached), with 4 items on it. Program 1, Program 2, ...3, ...4. The PLC i am using is a compactlogix...
Replies
5
Views
171
Hello All! Ok, we got a Work cell from a Integrator that is sending saved scanning data from the PLC to HMI (Panel View Plus) when I look at this...
Replies
3
Views
82
saludos a toda la comunidad Hace unos días he venido presentando pérdida de comunicación en una terminal hmi, anexo las imagenes de la secencia...
Replies
1
Views
106
Back
Top Bottom