versapro online monitoring 90-30 311 problems

nswu1

Member
Join Date
Oct 2005
Location
louisiana
Posts
278
I am able to go online with the processor and upload the program, but, when I click on monitor(either all,or page) I don't see any of the logic bits changing color. I am using versapro pro version V2.00, the PLC is 90-30 cpu 311. I configured the HW profile. Any suggestions?
 
1. Verify you are in RUN mode under PLC in the menu, anytime you Store or Load it will stop first.
2. Verify monitor is active.

Note: Some things can be modified online but some changes require a Store which will put it in stop mode.
 
Can you get to a "Logic Equal" state? You need to have logic equal before you can see the states of the I/O change. If it still says "Logic Not Equal" after uploading from the PLC to VP, you may have a version discrepancy. If that is the case, you will need to download from VersaPro to the PLC to achieve a "Logic Equal" state.

What I mean by a version discrepancy is that the program in the PLC was created with an older version of VersaPro than you're currently running on your PC.
 
Can you read "LOGIC EQUAL" on the lower right corner on the status bar?

Did you upload the Hardware configurations along with the logic?
 

Similar Topics

Using VersaPro software with GEFanuc PLCs, how can I make Online changes? I mean, in the Old Logicmaster I could change a rung, and the with ALT+S...
Replies
2
Views
3,229
I have a LM9030 program that is running on a IC693CPU331 that was installed in the mid 90's. How can I find out if this cpu can handle newer VP...
Replies
3
Views
1,262
I have a Versapro project file for a Versamax PLC. Need to identify what type of variables are suitable and made available for BMS system to...
Replies
3
Views
1,707
I was given a file with a .SwxCF extension. Can this be opened in any way with VersaPro? I only have version 2.0 Pro and have no luck. I think...
Replies
4
Views
1,953
I have GE Fanuc VersaPro 2.0 software where can I get an upgrade CD. I need to program a IC200UEX164 64 point (40) 24Vdc In; (24) Relay Out; and...
Replies
26
Views
2,199
Back
Top Bottom