I have a Profibus Network(Master - CPU 315, DP-Slave 4x ET200S+, KUKA Robot) Every time when one station falls out Master stops. How can I prevent that PLC goes to STOP or how can I force it to go automaticly to RUN?

Almost forgoten... I use S7:)
 
Last edited:
I haven't got my S7 machine at the mo so can't be precise. I would say you need one of the hardware fault OB's programmed in the PLC, you'd have to look up the OB's to find which one.

We use DP diagnosis blocks, that create an alarm but the system does not fall over.
 
Automatiker said:
How can I prevent that PLC goes to STOP or how can I force it to go automaticly to RUN?)
Hi
Add into S7-program following ob's -> OB82"I/O Point Fault 1", OB86"Loss of Rack Fault" and OB122"Module Access Error". Your PLC wouldn't stop again (only in the case of Profibus failure) :rolleyes:

-Pete- 🍻
 

Similar Topics

Hello, I am in possession of a WAGO PFC 200 750-8216 which I was successfully able to set up as a Modbus RTU Master to a slave device using...
Replies
0
Views
81
Does anyone have an example project of the cm ptp ET200 SP HA with 410-5H DCS (PCs7 9.1 SP1) for MODBUS MASTER/SLAVE communication ?
Replies
2
Views
128
if we need to take back up of Siemens CPU(s7300 /s7400) with non siemens slave profibus nodes without their gsd files and when we restore it in...
Replies
0
Views
82
Hello, I set up my Micro820 with a basic mapping. When I try to run a script to read the addresses I get errors for illegal addresses...
Replies
2
Views
169
HELLO MY FRİENDS ı have problem. ı tought you can solved thıs problem for me. First of all When I checked all the cable connections of the...
Replies
0
Views
402
Back
Top Bottom