Upon replacing a 120V prox I find that the PLC doesn't sink enough current to operate the prox. Is there a simple solution?
ShockJocky said:Correct on the sink source, should have said "draw". The prox won't enable the input. But when same prox is connected to a small cube relay it will close the relay. the prox has a rating of 5mA-300mA.
CroCop said:300mA or .3 Amps is more then enough to turn on a PLC input.
Something else is the problem.
JesperMP said:Just checked it myself.
It states that the input current at signal "1" is >0.08 mA.
So there you have it, the prox is incompatible with the PLC.
Easiest workaround is via a relay like you suggest yourself.
rsdoran said:Just a thought, you do have the neutral for the 120vac connected to the inputs?