Dear Forum
Do PLC manufacturers have specific commands / modules for input and output of standard TTL &(+5vdc) CMOS (+16vdc) control signals that are used to send a recieve control signals into integrated sub-systems hardware. I know that there are transistor and DC I/O modules but these all seem to be either for driving things or recieving sensor inputs. What about good ol' low current logic state intefacing ie. 74 series etc.



Cheers
PaulS
 
Some PLC manufacturers have them. They call them 5 volt or 5-15 volt modules.
The inputs are Optoisolators. Once I modified an Automation Direct module rated for 24DC input. The dropping resistor was 2200 ohms. I needed TTL for 2 of the inputs, so I changed the 2 resistors to 680 ohms. Normally, I would use the D2-32ND3-2 module.
The transistor output modules are also optoisolators, but some need the 24DC to power the output circuit. The closest I see is the 12-24 volt modules. That will work for CMOS, but you may need high current pullups to drive the opto's. Ive used relay modules for 5 volt outputs, sinking format to help with noise immunity.
Outside world interfacing will always be isolated (opto or relay) to protect the rest of the PLC. In the PLC world, an accidental short to 120vac blows only the module, not the entire system.

Go here to look at the modules for AD's DL-205 series PLC's.
 
Last edited:

Similar Topics

Hello all, I am trying to communicate to a brushed DC motor controller through a 1769-ASCII to a RS485/TTL serial adapter. Part numbers for each...
Replies
2
Views
1,476
Hi, Im a bit unsure about how to connect my SIEMENS encoder (5V TTL/RS422) To my baseunit (The light one).. I have attached a pic of how i have...
Replies
2
Views
1,529
We have a controllogix L72 whit DHRIO card reading a PLC5 rack that which we removed processor and replaced with 1771-ASB. the first slot is...
Replies
4
Views
1,587
Does anyone know of a DIN rail mountable rs-232 to TTL converter?
Replies
1
Views
1,979
I have a few quickpanels on some older equipment. Connected to GE Fanuc 90-30 PLCs. I have went through 4 of the MI-CAB-C49 cables over the past...
Replies
16
Views
3,791
Back
Top Bottom