re-post with details.
There are several different models of CompactLogix controllers.
Each model of CompactLogix controller has a different memory capacity and a different task capacity. The newest controller, the 1769-L43 with integrated motion control, has the most tasks (16), while the 1769-L31 controller has 4.
Any Logix-family controller can run only one Continuous Task, but the other tasks can be any mix of Periodic or Event type.
This Allen-Bradley catalog page describes some of the differences between CompactLogix controller models:
http://www.ab.com/en/epub/catalogs/12762/2181376/2416247/407648/
The web page behind that link includes the following information:
1768-L43 16 tasks (1 continuous task).
For the 1768 controller, Event Tasks can be triggered by Consumed Tags, EVENT instructions, axis, and motion event triggers.
1769-L35x: 8 tasks (1 continuous task).
1769-L32x: 6 tasks (1 continuous task).
1769-L31: 4 tasks (1 continuous task).
For the 1769 controllers, Event Tasks can be triggered by EVENT instructions and Consumed Tags.
What is missing from both of those descriptions is the ability to trigger an Event task from a discrete input. Because the 1769 Compact I/O bus has a fixed RPI of 2 milliseconds, there is no individual module interrupt function like there is in the 1756-series backplane. The 1769-BOOL module helps leapfrog this limitation with sub-millisecond I/O reaction times.
What's your application for event interrupts ?