Siemens module SM326 DO 10xDC24V/2A

radekg

Member
Join Date
Jan 2007
Location
Bristol
Posts
1
Hello,

I am looking for help about Siemens SM326 module.

I am trying to configure hardware for the following set:
CPU315F-2DP, CP340x2, SM322x1, IM360/361, SM326 DI24xDC24VCx2, SM326 DOxDC24V/2A using Step 7 5.3SP3 + package DS5.4 + F-config 5.5SP1
I have no problem in configuring any of the above mentioned modules except the last one.
In standard mode I get the following errors:

Diagnostic buffer of module DO10xDC24V/2A
Order No./ Description Component Version
6ES7 326-2BF01-0AB0 Hardware 3
- - - Firmware V 2.0.7
Rack: 1
Slot: 6

Event 1 of 1: Event ID 16# F580:8006
Module not Assigned Parameters
Internal error, Incoming event

In safety mode what I get is:
Diagnostic buffer of module DO10xDC24V/2A
Order No./ Description Component Version
6ES7 326-2BF01-0AB0 Hardware 3
- - - Firmware V 2.0.7
Rack: 1
Slot: 6

Event 1 of 3: Event ID 16# F980:8031
Loss of Communication
External error, Incoming event

Event 2 of 3: Event ID 16# F980:0201
Monitoring time for data message frame exceeded
External error, Incoming event

Event 3 of 3: Event ID 16# F580:8006
Module not Assigned Parameters
Internal error, Incoming event

I have simplified my program so that it is generally blank (not to influence hardware).
I get the same errors on three other SM326 DO10xDC24V/2A module instances so the problem should not be with the hardware.

I have looked on any parameters that I could set in the modules:
- in standard mode the bottom switches are set all to 0/ in safety mode they are set to the address
- diagnostic interrupt: does not influence the error
- disable light test: does not influence the error

Simplifying PLC to CPU315F-2DP + SM326 DO10xDC24V/2A (no other modules installed) does not solve the problem.

Does anyone have any idea/experience what should I do in this case?
Thanks and regards
Radek
 

Similar Topics

Hello everyone, I've had this issue for the last 2 days where I try to assign the profisafe address to an IO block (6ES7 146-6FF00-0AB0) but when...
Replies
5
Views
141
Hi! Doing a lab project with two 1214FC. Got a warning about reintegration of modules wasn´t configured and tried to do that. Found the two...
Replies
3
Views
811
I have a 6ES7 421-7DH00-0AB0 card with the INTF LED illuminated red. This internal fault on the card is preventing the CPU from going into run...
Replies
1
Views
1,127
On the Siemens IM153-1 Interface Module, ET200M, what is the difference between the "0 X-18/19/20" and the "1 x-8/9/10? Picture attached of the...
Replies
1
Views
1,280
Any manufacture recommendation for remote I/O for Siemens PLC.
Replies
10
Views
2,933
Back
Top Bottom