I’m thinking seriously about replacing all or part of a BMS with PLC based system. Any tips and insights would be appreciated. Sorry about the long post but I think some background is necessary.

Background:

Our factory got hundreds of AB PLCs and also a BMS (Building Management System) that’s based on Siemens Apogee system with an Insight Interface (a type of HMI and programming tool). The BMS controls the lights in the factory and the HVAC for both the plant and the office areas.

Due to missteps in the past, the BMS network wiring is quite screwed up. The BMS network consists of two levels, the BLN (Building Level Network) and the FLN (Floor Level Network). The BLN is on the Ethernet physical network (not sure about the protocol) but the FLN is some type of serial network. The FLN is what link all the devices together.

To get this system functioning correctly, we have to go through the entire network to find dead-points, clean up the programming, fix mis-wired FLN points, etc.. No matter how I look at this, it will be a lot of work. We also pay a yearly support agreement to Siemens similar to the Rockwell deal that includes a few hours of support (and you think Rockwell is bad) and software updates.

My thinking:

It’s easy to change the lighting controls, etc to PLC control. It can be Micrologix 1100, Flexlogic, or Compact Logic with digital I/O. Due to already heavy presence of AB equipment I don’t see a lot of benefits to go with other PLC.

The single biggest problem with going with PLC is the office HVAC control. Office air duct are controlled with VAVs (Variable Air Volume device), http://en.wikipedia.org/wiki/Variable_air_volume which is basically a damper. VAV got a specialized controller called TEC, that measures pressure drop (air volume), temperature of the duct, temperature of the room, and actuate the damper. Some VAV also includes heating coils.

This TEC unit only cost about $1k. Yup, that’s right. To replicate the same funcationality with a PLC would be costly; PLC, DI, DO, AI, AO, pressure sensor,… ouch.

Solution?

- I am thinking of keeping these TEC units but someone controlling them with a standard HMI. I have no idea what can convert the FLN to standard protocol, any idea? I doubt Siemens will lend me much help swapping out their system.

- Alternative is to swap out the TEC with another VAV controller that talks standard industrial protocol, suggestions?

- Do this with a cheaper PLC than AB but I will need analog IO.

Some past topics:

http://www.plctalk.net/qanda/showthread.php?t=28389&highlight=bms

http://www.plctalk.net/qanda/showthread.php?t=14882&highlight=bms
 
What brand are the VAV's? If Enviro-Tec then may be able to contact them direct for assistance with the controller.

If you can get the info on the VAV controller then may find out the protocol to communicate with a PLC or determine the specs for the sensors etc and change over to a plc.
 
Good article

I found a great article via google at www.appa.org (A organization for educational facilities professionals). I thought I share that with the rest of you:

https://www.appa.org/files/PDFs/Taking%20Back%20Control.pdf

Excerpt:

..extra cost is controlling VAV systems. The cost of using a PLC for every VAV terminal unit is prohibitive. This expense is due to the distributed nature of VAV input/output
However, they found a way around this but they didn't elaborate.
There is a terrific business opportiunity if PLC manufacturer were to build a small VAV controller..
So, any PLC maker want to take on this challenge? :)

I'll see if I can get hold of the author of the article to give me any pointers.
 

Similar Topics

I am working on a project where I need to create a visualization screen (HMI Panel or PC) using wincc tia portal v16. It will be connected to the...
Replies
3
Views
616
Are there any HMIs besides C-More that offer a driver for the Automation Direct Productivity series PLCs? Running into some issues with C-More and...
Replies
10
Views
1,574
Got an old machine with a IC610CPU104 CPU. A bit of research told me this is the same as DL305 so DirectSoft from AutomationDirect should work...
Replies
15
Views
2,145
I need some clarifications from VFD experts. I have a project with a vibratory conveyor that must be stopped relatively quickly. Stopping is once...
Replies
2
Views
808
Hello all. I have a parts elevator in a very dirty environment. I have used VFD's a lot over the years but I have never had to have one with a...
Replies
11
Views
1,843
Back
Top Bottom