micrologix 1200 - "first pass" problems

Boomer

Member
Join Date
Feb 2007
Location
cph
Posts
5
heey ppl. I have a problem with a micrologix 1200.


My "first pass" (init) don't work.. it dosent make the



thanx :)
 
I think you're saying that it isn't on at the time of your screen-print. Right???

If so, you're never going to see the first-scan bit come on. It's only on for the very first scan of the PLC, then it's off.
 
If you really don't believe that the S:1/15 (First Pass) bit is working, then you will need to create a rung that will latch this state.

In your example, Rung 0007 will latch up B3:1/1 on a first pass as long as B3:0/0 remains ON and B3:0/9 remains OFF.

....

I would bet the cost of your controller that the First Pass bit is working just fine. You just need to understand fully how it works.
 

Similar Topics

Hi everyone, I'm working on a project where I need to exchange data between a Siemens S7-1200 PLC and an Allen-Bradley MicroLogix 1400 PLC. The...
Replies
8
Views
651
I have a MicroLogix 1200 that has an 8 input and a 16 output. Every 6 months-year I get a fault and when online go to error it is something like...
Replies
3
Views
506
Have a bad output on a Micrologix 1200. Moved wire over to an available output, changed program to associate with new output. downloaded program...
Replies
8
Views
753
I need help achieving the following task: ML1200 sending 4 to 20 mA thru analog output ch0 to a DC speed controller analog input(4 to 20 mA) my...
Replies
3
Views
671
Hi there I am new with this thing and i don't know how to connect Allen Bradley Micrologix 1200 PLC to Raspberry Pi using USB to RS485 in NodeRED...
Replies
3
Views
2,278
Back
Top Bottom