i have the module AI 6es7 331-1kf01-0ab0 but it is not accessible in simatic manager v5.2 software. i need gsd file for it

thanks
 
Hi ismail.

Is the module placed in an ET200M rack that is connected to the CPU via Profibus ?
Or is the module sitting in the S7-300 "rack" ?

If it is the first, then you can download GSD files for all Siemens ET200M modules from http://support.automation.siemens.com/WW/view/en/113498

If it is the latter, then you have to upgrade your STEP7 version. I think the ability to update the HW catalog came with v5.3. The current version is v5.4
 
http://support.automation.siemens.com/WW/view/en/23183356

The Hardware Support Packages enable you to configure modules that are not included in the Hardware Catalog of your STEP 7 installation.
As from STEP 7 V5.2 onwards, you can use the Hardware Support Packages to update your existing Hardware Catalog.

http://support.automation.siemens.com/WW/view/en/22374877

3i(2005_11_07)STEP7_03_e.gif
 

Similar Topics

Hello everyone, I've had this issue for the last 2 days where I try to assign the profisafe address to an IO block (6ES7 146-6FF00-0AB0) but when...
Replies
5
Views
207
Hi! Doing a lab project with two 1214FC. Got a warning about reintegration of modules wasn´t configured and tried to do that. Found the two...
Replies
3
Views
828
I have a 6ES7 421-7DH00-0AB0 card with the INTF LED illuminated red. This internal fault on the card is preventing the CPU from going into run...
Replies
1
Views
1,145
On the Siemens IM153-1 Interface Module, ET200M, what is the difference between the "0 X-18/19/20" and the "1 x-8/9/10? Picture attached of the...
Replies
1
Views
1,293
Any manufacture recommendation for remote I/O for Siemens PLC.