I have to size a replacement motor starter with limited info . i have the hp 75 and voltage 240 . but nothing else . what is the formule for sizing overloads ? can it be done with htis limited info ?
 
75 Hp is 55 KW. I presume its three phase, given the size. Phase current aprox 192A. That is from a chart i have. most motor, overload manuf. have them on their websites.
 
75 hp => 75*0.75 = 56.25 kW
55 kW/380V/1500 RPM => In = 106 A => In240V is around 168A
So In is around 172 A for 75hp/1800 RPM motor.
 
Is it a motor, or a gear-motor combination ?

I use SI units to convert like this:
I = P / (U x 1.73 x Kpf)

I is the line current (in the phase) in A.
U is the line voltage (between two phases) in V.
P is the rated shaft power in W (not kW or hp).

Kpf is a the power factor.
For small motors it can be as little as 0.55.
For bigger motors it can be up to 0.85
If there is a gear in between the motor and the outlet shaft, then you have to account for the efficiency of the gear as well. It can be as low as 0.60 for some gearmotors. So for smaller gearmotors it becomes somewhat of a gamble to only rely on some vague shaft power rating.

edit: For a 55kW/75hp motor my charts say approx 0.72 for the power factor. That gives I=184A.
 
Last edited:
it is a motor only . not sure about the load specs . do the number of poles factor into these formulas ? and what is the formula to properly size the overloads . sorry for all the questions .i am begining work in the field while going to school for controls
 
Yes the number of poles do matter, but my formula only accounts for 4-pole motors. I dont have something for 2- or 6-pole motors right here and now.
An overload should be sized to exactly the rated motor current.
 
I carry a sliding "pocket engineer" developed by Buss (the fuse company).

It says for 230v, 3ph, 75hp, 1800rpm, squirrel cage, induction motors, the FLA is 192. It often errs on the high side.

The best source of info is the nameplate, the next would be the manufacturer.

Do you have any historical "full load amp" measurements to refer to?

Solid state overloads are set to FLA. Try to select an overload block with your FLA somewhere near the center of the range.

"Heater element" type overloads are selected from the manufacturers chart.

(I admire your education/work ethic)

Stationmaster
 
thanks for the info . the motor in question has no nameplate .apparently one of the maintenance guys removed it with a chisel to order a new one instead of writing down the info . i got the info i have from an old print in the machine . thank you for all the replys . very helpful
 
A rule of thumb is that FLA on a 460 VAC 3 Phase motor is 1.25 x hp. For 230 VAC it would, of course, be 2.5 x hp. Don't use this for sizing heaters, though.

If you can't get nameplate data, use the starter manufacturer's charts or the UL tables. Note, however, that old and new motors can have big differences in nameplate FLA. There can be quite a range, so make every effort to get the right motor data sheet. Also note that some motors have a 1.15 service factor, which can give you some margin for error, but that isn't universally true.

Number of poles affect efficiency and power factor,but this ins't reflected in many starter sizing charts.
 

Similar Topics

Good Morning , We have a 100 HP , 480 V (Full Load Amps 124 ) Hammer Mill motor that has a Wye/Delta starting procedure. I would like to put...
Replies
16
Views
4,283
Hello all, Well I am going to throw this out here just to get a general consensus of others thoughts of this subject. We are going to do a...
Replies
14
Views
3,956
I need to setup a motor circuit for what is now a 30 HP motor and will be a 40 HP soon. I am using a 100-C55 Allen Bradley contactor and the E300...
Replies
19
Views
5,650
Hi, In my plant, we use a few Lab mixers for stirring-up chemicals and mixing them. Some of the mixtures, nearing their mixing times, can...
Replies
3
Views
4,427
Hi all, I have spent about 3 days after hours searching around the net and I have picked up enough information to order a 3kW 8 pole for an AC...
Replies
30
Views
10,036
Back
Top Bottom