Regarding the rate measurement capability of the Allen-Bradley 1769HSC - according to the datasheet, it can handle up to "4 channels of pulse/count inputs", but it is not clear on exactly the operation mode of these inputs.

I require 4 channels of frequency measurement of pulse input (single direction only). Is the HSC capable of this?

It would also be desirable to get a counter reading as well as a rate measurement for each input. Is this also possible?

Thanks in advance
 
Go to pages 2-18 up to 2-21 of Publication 1769-UM006A-EN-P and you will find the answers to your questions, you can download it from AB web page.
 
Last edited:
It seems to me as though the counts and rates are stored in different registers; Local:<x>:I.Ctr<y>CurrentCount and Local:<x>:I.Ctr<y>CurrentRate respectively.

One reason I ask this question is that other brands, Telemecanique for example, allow four pulse inputs in counting mode, but when those same inputs are used in rate measurement mode the number of inputs drops to two. Further, a frequency meter can not give a total count value, and a counter can not give a rate value.

When the 1769HSC is used in RATE mode, are all four inputs still available? And, though not absolutely necessary, can the total counts be read directly from the register also?
 
Thanks widelto,

I do not quite understand what the user manual is saying though. It seems to me that what I want to do is possible; I would just like some confirmation!
 
Yes, it is possible, and those counters can have independent rate mode update times as well. (slot:C.Ctr<#>CyclicRateUpdateTime)

But, of course, that is on a Logix platform. What platform are you using?
 

Similar Topics

Hi, I have the 1734-IJ 5V DC Module connected to my allen bradley PLC. My current hardware outputs a 5V DC Square wave and I want to read the...
Replies
1
Views
1,556
Maybe you guys can help me with this. I have a customer who purchased a cutoff system and is now setting it up at his facility. The system has two...
Replies
12
Views
6,608
Hi, The hardware is: Click Plc model # CO-O1DD1-O HMI model # S3ML-R magnetic-inductive flow meter model # FMM100-1001. I will set the flow meter...
Replies
4
Views
136
I have been looking to this and thought I'd ask for input from others before I take it in a wrong direction. The guy who used to set these up...
Replies
9
Views
404
How can I integrate my S7-300 Simatic with the IFM AS-i Master AC1335 and its slave IOs, such as 2411 and Airbox 2041, into Simatic Manager?
Replies
0
Views
116
Back
Top Bottom