Is the A1 and A2 on a contactor the coil to trigger the contactor from the output of a plc?
Lancie1 said:A less-desirable alternative is to have the overload wired back to the PLC as a fault input, so that the PLC then turns off the contactor.
Lancie1 said:A less-desirable alternative is to have the overload wired back to the PLC as a fault input, so that the PLC then turns off the contactor.
leitmotif said:Lancie
I am curious why you say it is less desirable to have motor overload as an input to PLC.
GRANTED if they are in series with coil the coil drops
the aux contact opens (and if wired to PLC) would tell PLC motor tripped
BUT PLC would have no idea why.
IF overloads were wired into PLC then it would have idea and could put motor trip warning on HMI etc etc.
It would take another input (or threee ??) of course which is the downside of doing it this way.
Like to hear your thoughts
Dan Bentler
BobB, tell me you don't mean this as it reads! If you do, you need to go back and take another look.BobB said:I do not use overloads anymore at all but use motor circuit breakers instead with plug in auxiliary contacts.
I am not talking about a contact in series with the PLC output, but an overload contact at the motor starter that shuts off the contactor upon motor overload. I am sorry to disagree, but if I only have one overload contact, it always goes to provide safety of the equipment and personnel. If the PLC doesn't know the motor has tripped, too bad. I can live with that, but not with burning down the plant. Running the overload function to the PLC FIRST (and considering the PLC as the overload controller) is not good design. You are adding another failure mode to a vital safety device.You should always have a signal from the overload to the PLC input, regardless on whether you also use a contact in series with the output.
Lancie1 said:I was talking about the case where you have only one motor overload contact.
Steve Etter said:BobB, tell me you don't mean this as it reads! If you do, you need to go back and take another look.
Overloads are intended to monitor for sustained overload situations such as those occur as a result of loose connections or insulation breaking down over time. Such overloads tend to cause heat build-up but may not cause an overcurrent situation.
Circuit breakers are intended to monitor for instantaneous overcurrent situations such as short circuits. These tend to be very sudden such that overload detection devices cannot respond quickly enough to prevent significant damage.
Clearly, a correctly designed motor control circuit needs to have both overcurrent and overload protection and, unless you have a device that is designed to do both, they are two separate items. If you are attempting to use a circuit breaker in place of an overload detection device, you have created an unsafe condition.
Steve