Question re: need for line side contactor for an Automation Direct GS20 VFD?

ControlSysNick

Lifetime Supporting Member
Join Date
Jan 2009
Location
Ontario
Posts
54
I'm using an Automation Direct GS20 VFD for the first time and I have a question for the Automation Direct gurus regarding the recommendation of a contactor on the incoming AC line power. According to the manual:

"The addition of a magnetic contactor (MC) in the AC line power input wiring is recommended to turn off power quickly and reduce the possibility of malfunction if the protection function of the GS20(X) AC drive is activated.".

I intend to use the STO function with the E-Stop and this application does not require cutting the power to the drive in an E-Stop situation.

From what the manual says, the purpose of this line-side contactor is to protect the drive if the "protection function of the GS20(X) AC drive is activated.".

According to the manual, the protective function is activated in an overload situation. Would it not be enough to monitor a relay on the the drive for an overload condition and just turn off the run signal if an overload occurred? Or do you always have contactor on the 3-phase AC line power ahead of the drive?
 
I really dont like putting line contactors before the drive. I have seen many drives fail because power is removed the whole time especially while running.
We use magnetic circuit breakers which gives a point to isolate and also protects against short circuits on the drive. For me the drive should handle the load side by itself
 
Hi Chud,

Thanks replying.

Like you, I think the drive should be able to handle the overload situation gracefully and it shouldn't be necessary to cut power on the line side.

However, the manual appears to suggest that it may be necessary. I've attached a screen grab from the Automation Direct GS20 Drive manual.

I'm inclined to interlock the RUN signal to the drive and not install the line side contactor and I think it will be fine. However, as I'm new to the Automation Direct GS20 drives, I was wondering what the folks that use and know these drives would do. Do you use these drives without the line-side contactor and have no problems?

Thanks again!

Nick

GS20-Wiring-Showing-Recommended-Contactor-and-Interlock.png
 

Similar Topics

I have a few PLC questions that are on my test and there are bonus questions but I would like To get some help on answering them because I would...
Replies
7
Views
3,117
So the quick and short of the situation is that I designed an axle press that was sent to one of my company's other facilities. That facility just...
Replies
19
Views
4,248
Does a hardwired 120 VAC machine need a local disconnect and lock out device? I was always under the impression that it did, but a plant controls...
Replies
4
Views
2,099
So ive chosen the first option. Is it correct? it would be helpful If i could get an explanation too. thanks
Replies
7
Views
2,265
We use Siemens WinCC flexible 2007 for HMI. In the HMI in one screen when one object pressed a faceplate open. In the faceplate many object there...
Replies
2
Views
1,849
Back
Top Bottom