Safety relais

ivo.maenen

Member
Join Date
Nov 2003
Posts
663
If you have a safety circuit with e.g. K1&K2 controlled by the safety-relais. Do you use the NO-contacts of K1&K2 to kill the power of the control-circuits or do you use them to kill the power of the power-circuits?

In my opinion killing the power of the power-circuit should be safer but then you also need more powerfull relays. For safety-reasons this should be no issue. But I never saw this in the schematics what I could lay my hands on. Maybe it is also dependant of the safety-cat. Can somebody comment on how you do this?
 
I always use K1 & K2 to kill both the control power (the feed to the output cards) and the power feeding all the motor contactors. If you only kill the control power, you could have a case of a contactor welded closed and still feeding power to a motor/pump/etc. If you cut the power to the motor contactor, it wouldn't matter if it welded or not.
 
side note on that in some cases you need a controlled stop on certain types of equipment the machine should have a risk assessment done to describe what category you require for safety ie cat 1 or cat 3 in cat one a weld can cause a problem on the cat 3 standard you would use multiple NO contacts on each senser and pushbutton so that a single weld does not prevent a proper shutdown. I'll do a search and find the link I've posted pevious with an excelent article on the seimens website
 
It is application dependant so evaluate machine design etc to determine risks and select proper category but when you kill something (actuator etc.), i always kill motive power, period.

Killing power instantly may be a problem in some cases since motion need to be stopped before power is removed. There are solutions for that (in both hardwired safety and safety plcs). For example one can introduce delay (Safety!) for killing supply power but pulse trains to Drives are stopped immediately.

Safety integrated from Siemens is just Siemens name for same thing that others also have (like AB for example) and provide means to save on those big contactors (equivalent is at least partially integrated into drive design).
 

Similar Topics

After some interesting conversation regarding the safety of emergency stops, I saw some posts talking about the safety standard conversation...
Replies
21
Views
419
Hi, I am using AB 5069-L306ERS2 CPU. My system should achieve SIL-2. I have safety door switches connected to AB 5069-IB8S module, and I want to...
Replies
1
Views
108
I'm struggling to get an FR-E800SCE to work on CC-Link IE TSN. I'm sure the issue is with the drive, when I plug in the network cable I get no...
Replies
1
Views
103
Hi I have a yaskawa gp7 robot arm which I am going to use for machine tending with a cnc mill. Is it a good idea to buy a SICK laser scanner for...
Replies
5
Views
237
Power flex 527 Network based safety drive had faulty and alarm pop up SOS Code internal fault Unable to set or clear the fault manually or...
Replies
5
Views
115
Back