Ive got an ML1100 setup as Modbus RTU Master, through a B&B RS232-485 converter. I have 3 power transducers (Multitek M550), on the network, along with a Hitachi SJ200 -HFU75 VFD.
I have 7 MSG instructions to move data as needed. One each MSG instruction to read 32 elements from each transducer. The other 4 messages are for the VFD control, 2 writes and 2 reads. In normal operation, the VFD MSG'ing is working fine, it communicates and I have control. However, the three transducers will not communicate. When I have only one of the transducers (remove all other messaging, I can see the transducer. As soon as I add another transducer MSG, it will stop communicating with all transducers. Ive tried to "cascade" the MSG instructions, but as soon as the cascade gets to an error'ed MSG, it stops.
I can hook up to the 232/485 converter, and using Multitek software, talk to each transducer with no issue, and I verified the ID#, Baud, Stop Bits and Parity are all correct.
Ive noticed that im getting an error 37 "Message timedout in local processor". It will clear when the MSG is re-enabled, but then error out shortly after. This happens on all the trasducer MSG instructions.

I have a few questions;
-Is there a limit to the number of MSG instructions I can have in Logix500/ML100?
-Can they be executed in order at the same time (by rung scan)?

Im scratching my head, as it doesnt make sense why its not working. I can only think that the timeout error means something with my MSG instructions isnt correct.

My original program is attached. The REV_A is an example of my original MSG instructions, but it would have all 7. REV_D is my current attempt to "cascade" the messaging, one at a time. Any insight or comments would be greatly appreciated!

Thanks
NH
 
nhicks said:
I can hook up to the 232/485 converter, and using Multitek software, talk to each transducer with no issue, and I verified the ID#, Baud, Stop Bits and Parity are all correct.
NH

Just to clarify whats above. Does this mean that you have communicated from your laptop/pc to ALL transducers at the same time ? Eliminating any cabling issues ?

In the past I have used an application called "Simply Modbus" to help setup Modbus comms (funny how a standard comes in sooo many slightly different variations). it displays some details on response time etc. it may be worth a try. The demo will let get online to test for a shortwhile.

2008-01-25_071508.jpg
 
As a followup - after checking the knowledgebase, we changed the Handshaking to None(485 network), and added a 50ms Pretransmit delay. We also put the 4 VFD commands on a 4 second timer, and the 3 xD's on there own 2 second timer. The VFD is talking like a champ, but the transducers are having issues. They are still returning an error 37, but occasionally, a message will make it through just fine.
Im trying to figure how to run the 3 xD MSG commands, and when they are done tx/rx, THEN move to the 4 VFD commands. Not pull the plug at the end of the 2 second timer.
Any help with this would be appreciated!

NH
 

Similar Topics

Hello all, I am trying to setup my MicroLogix 1100 as a modbus RTU master for a modbus network containing multiple modbus RTU slaves. I currently...
Replies
7
Views
3,927
Hello, i have a micromotion flow transmitter communicating with a ML1100 plc via modbus over channel 0. i am messaging to read data from the...
Replies
6
Views
2,448
So I have an ABB TotalFlow uFlo G4 unit and have configured it's COMM port as Modbus Slave. I have also mapped internal 32Bit Float Registers to...
Replies
9
Views
5,828
Hi all. I have some problems with ML1100 and modbus rtu, I have 2 nodes with solcon HRVs soft starter and MPS3000, ML has 1763-NC01, the ladder...
Replies
13
Views
5,449
I have a AB ML1100 that I am using to collect data from a device sending data over Modbus TCP/IP. From what I understand I will have to use the...
Replies
0
Views
1,764
Back
Top Bottom