ML1100 as Modbus RTU Master
CQ21
Apr 2021
Columbia
61
Hello all,
I am trying to setup my MicroLogix 1100 as a modbus RTU master for a modbus network containing multiple modbus RTU slaves. I currently have RSLogix500 (ver: 5.2) and want to know if this setup is possible with the software I have? If so, could anyone point me into the right direction on how to make this possible?
Also, my modbus slaves use the RS-485 electrical interface...how will this work? I heard the ML1100 has 3 channels: one ethernet, one RS-232, and I'm not sure what the last one is...If anyone could help, thanks in advance!
With rs-485 signaling, it will depend if your devices are 2-wire(half duplex) or 4-wire(full duplex).
But basically you just tie your Data lines to each other (A to A, B to B) and terminate at the end w/ a typically 120ohm resistor.
Thank you! It is a half duplex I believe. I was planning on using the 1763-NC01 cable and plug it into channel 0 and wiring my network from there. Would this work? The termination resistor goes across A to B correct?
The 1763-NC01 is right. It has a pin named TERM that allows you to add proper termination by connecting it to pin A.
You can get a slightly less expensive aftermarket 1763-NC01 from a forum member here. I have used his version and I like it better. You can actually read the text on the terminals in a dark panel much easier than the A/B version.
https://www.plccable.com/allen-brad...485-cable-8-pin-mini-din-to-6-pin-micrologix/
As always, RS485 vendors never quite do things the same way.
I think that you should be able to connect a MicroLogix 1100 to this Danfoss superheat controller using a 1763-PM01 cable.
The MicroLogix 1100's RS485 signal is not isolated from the rest of the logic. The "COMMON" terminal is the same as is used by the RS-232 port, and it should be connected to the DC Common of the controller's power supply as well.
The Danfoss EKD RS485 signal also looks like it's not isolated, and there is no Signal Common connection.
Because so many devices use the Shield of the cable as signal common, I would jumper COMMON to SHLD on the 1763-NC01 side.
The Data A and Data B signals might be correct to connect them "A-A" and "B-B". But with RS485 you never really know until you try.
I have a lot of good things to say about the CommFront product "HUB-485-4", which takes one RS485 or RS232 port input, and converts it to four isolated RS485 ports on the other side.
https://www.commfront.com/collections/rs232-rs485-rs422-ttl-serial-repeaters-hubs?variant=9077058115
I used this with a MicroLogix 1400 Series A controller a few months ago to connect its RS-232 port to four servo controllers that had themselves an RS485 port. This machine installation was notorious for noisy communication links, and the isolation on that device made it a non-issue. $150 to not have to worry about port isolation is cheap.
If I was doing this project I would probably use one of those and the SLC-5/05's Channel 0 serial port set up as a Modbus RTU Master.
But failing that, one of the browser-configured network gateways like the Spectrum Controls or RTA units would be my choice.
Hello, i have a micromotion flow transmitter communicating with a ML1100 plc via modbus over channel 0. i am messaging to read data from the...
2,449
So I have an ABB TotalFlow uFlo G4 unit and have configured it's COMM port as Modbus Slave. I have also mapped internal 32Bit Float Registers to...
5,834
Hi all. I have some problems with ML1100 and modbus rtu, I have 2 nodes with solcon HRVs soft starter and MPS3000, ML has 1763-NC01, the ladder...
5,450
I have a AB ML1100 that I am using to collect data from a device sending data over Modbus TCP/IP. From what I understand I will have to use the...
1,766
I am using Micrologix1100 as Modbus slave and Honeywell dcs as Modbus mater. ML1100 communication parameters configured with the Channel0 are as...
9,020