Yes there is an Import, its not 100% depending how the PV has been programmed. I just did a 1400 (not e) to PV+ on saturday, this took me 6 hours in the office and 3 hours on site.
Heres a list from the help of unsupported 1400e objects
Unsupported PanelBuilder 1400e Objects and Features
PanelBuilder “e” Settings and Controls not converted to Machine Edition
Transfer Inhibit control
Request control
Transfer Status control
Controlled Relay control
PLC Controlled Audio control
Message control
Message Handshake control
Polarity control configured to display a minus sign with a negative number
Acknowledge to PLC control (if the Alarm Acknowledge is set to Bit)
Remote Alarm Operation Hold Time; the
1400e Remote Alarm Ack Control Hold Time will be used for all alarm hold times.
Remote Alarm Control Delay Time. If an Ack control is assigned in FactoryTalk View, there is no delay time between the alarm acknowledgement and the Ack control being set.
Bit alarm acknowledgement
Blinking alarm messages
Alarm relays
Screen security settings. FactoryTalk View uses a different method to assign security to displays.
Date and time settings. ME date and time settings are based on the run-time locale settings, which will have to be set after conversion.
Any characters in PanelBuilder screen names that are invalid in ME will be replaced with an underscore "_" character.
Expressions; because some PanelBuilder 1400e expression syntax is not supported in FactoryTalk View Studio, all PanelBuilder expressions are disabled during conversion.
PanelBuilder “e” Objects not converted to Machine Edition
Scrolling List Object - including Cursor List, Multistate Indicator Object List, Local Message Object List, and Numeric Data Display Object List
Set Bit Cursor Point
GoTo Configure Mode Button
Here is a link to RA's example migration from 1400e to PV+.
The pdf explaining this is RA KB Article ID 44265 (Although the page wont load for me at present)
Put in
Migrating PanelView Enhanced Terminal Applications in the KB Search engine and it will be first hit.
I was lucky on the 1400 as all i had to change was the alarms, reason it took so long was as the new PV+ has a bigger screen with more functions and buttons i moved things around as the old PV app on the PV+ looked a bit of a mess (ie buttons didnt line up to the keypad, text was old PV format and small etc) although did function correctly.
If you post the PV 1400e program i (or someone here) will run it through the import and post the log file back of import errors.