Panelview Multistate showing question marks when I convert to french

daviper1996

Lifetime Supporting Member
Join Date
Jun 2010
Location
roseville
Posts
16
I recently added several new screens with multistate indicators. While in English they are fine. When I switch to French they turn to question marks. I thought since they are only numbers it would not be an issue. Is there a work around or will I need to change objects?

Thank you
 
Solution

I looked around some more and found the option in Menu / Tools / Languages

Check "Display undefined strings using the default language"

This kept my numbers displayed on the indicators for both English and French.

Hope this helps someone or even myself in a year or two!
 