bkstump
Member
I've got a 1771-L20E processor sitting in Chassis 0, with channel 1B daisy-chaining to another 12-slot chassis configured as chassis 3, and finally, a Panelview 1000 at the end of the RIO chain as "last chassis" (and terminated).
All chassis are set as 1-slot addressing.
Configured addresses are as follows:
Chassis 0: x:000/00 - x:010/17
Chassis 3: X:030/00 - x:037/17
Chassis 2 (Panelview): X:020/00 - x:027/17
Chassis 3 contains a 1771-ASB (series B) in the left-most slot.
Chassis 3 IO slot assigments are as follows:
Slot 0: 1771-IBD
Slot 1: 1771-OBD
Slot 2: 1771-IBD
Slot 3: 1771-OBD
Slot 4: 1771-IBD
Slot 5: 1771-IFE/A (set as single-ended)
Slot 6: 1771-IFE/A (set as differential)
Slot 7: 1771-IFE/A (set as single-ended)
Slot 8: empty
Slot 9: empty
Slot 10: empty
Slot 11: empty
The right-most slot contains a P4 power supply module.
All input modules as well as the ADC modules appear to be functional.
Here's the problem:
None of the output modules (1771-OBD) will go "Active". The 1771-ASB module's green "Active" indicator blinks at a slow rate, and the "Adapter Fault" and "I/O Rack Fault" indicators are always OFF.
I have tried everything I can think of. I'm stumped!
Thanks,
James
--
James R. Graham
Controls Engineer - IU Cyclotron Facility
email: [email protected]
All chassis are set as 1-slot addressing.
Configured addresses are as follows:
Chassis 0: x:000/00 - x:010/17
Chassis 3: X:030/00 - x:037/17
Chassis 2 (Panelview): X:020/00 - x:027/17
Chassis 3 contains a 1771-ASB (series B) in the left-most slot.
Chassis 3 IO slot assigments are as follows:
Slot 0: 1771-IBD
Slot 1: 1771-OBD
Slot 2: 1771-IBD
Slot 3: 1771-OBD
Slot 4: 1771-IBD
Slot 5: 1771-IFE/A (set as single-ended)
Slot 6: 1771-IFE/A (set as differential)
Slot 7: 1771-IFE/A (set as single-ended)
Slot 8: empty
Slot 9: empty
Slot 10: empty
Slot 11: empty
The right-most slot contains a P4 power supply module.
All input modules as well as the ADC modules appear to be functional.
Here's the problem:
None of the output modules (1771-OBD) will go "Active". The 1771-ASB module's green "Active" indicator blinks at a slow rate, and the "Adapter Fault" and "I/O Rack Fault" indicators are always OFF.
I have tried everything I can think of. I'm stumped!
Thanks,
James
--
James R. Graham
Controls Engineer - IU Cyclotron Facility
email: [email protected]