Irondesk, I am sure you know that 24 AWG is smaller wire than 18 AWG. Be sure to get a written statement from the customer saying that "24 AWG is approved to use for all 4-to-20 miliampere signals". If any signal loss (or wire breakage) problems arise later, pull out the statemenet and pass it around again.They said they use 24 awg for all 4-20 ma wires.
irondesk40 said:Good Info
Another question that relates to this.
Have a installation that we will be doing in China, and some of the 4-20ma signals will be about 30-40 feet away.
The China plant engineering people are asking what size wire we are planning for this.
In the best, I have always used Beldon 18awg shielded cable, but the sensors is usually only a few feet away from the panel.
They said they use 24 awg for all 4-20 ma wires.
Is there a certain quide or wiring code that deals with 4-20ma signals and conductor sizing, etc.
I did some searches on the web and this site, but nothing useful yet.
Bob A. said:I have run 4 - 20 loops over #24 single strand telephone wire for as much as much as 4 miles, which is about the limit. If you think of your loop transmitter as a constant current regulator, then the open circuit voltage is the ultimate limiting factor as to how far you can go. So if you start with 24 VDC open circuit and you want to push up to .020 Amps, 24 VDC / .020 = 1200 Ohms. So you must design a system that does not get near 1200 ohms, or you will run out of voltage at the high end of the control range. (It could become a 4 - 19 mA Loop)
Remember that your wire goes out and back and make certain of your available open circut voltage.
Check out the wire calculator at this link:
http://www.cirris.com/testing/resistance/wire.html
Best Regards,
Bob A.