I am using a simple program like this

%I0.0 %Q0.0
|--||------------------------------()--|

I am using an RS232 cable for the connection with the plc just for checking the connection whether it works or not. I connect it with the PLC and it shows me the PLC inputs, outputs and run error and state LED's on screen of the computer. The Run is blinking when I press run it doesn't show me the output or input status. Means the LED's are not ON even on the monitor of the PC nor on the PLC. I made the connections like this.
+24V connect to the DC IN COM. using a switch connecting it's one side with the DC IN COM and the other side with the input terminal 0, and for the output I am using a multimeter to check the status of the output. But there is no response.
The PLC that I am using is a TWIDO TWDLCAA24DRF, and the software I am using is twidosoft. Please help me in solving the problem.
 
There are two things that can cause the problems here. One is if in your settings you have the wrong PLC configured. The other is once you have loaded the program in at least upto V3.0 you had to go and manually change the plc back into run mode. just some things to look into.



sharks said:
I am using a simple program like this

%I0.0 %Q0.0
|--||------------------------------()--|

I am using an RS232 cable for the connection with the plc just for checking the connection whether it works or not. I connect it with the PLC and it shows me the PLC inputs, outputs and run error and state LED's on screen of the computer. The Run is blinking when I press run it doesn't show me the output or input status. Means the LED's are not ON even on the monitor of the PC nor on the PLC. I made the connections like this.
+24V connect to the DC IN COM. using a switch connecting it's one side with the DC IN COM and the other side with the input terminal 0, and for the output I am using a multimeter to check the status of the output. But there is no response.
The PLC that I am using is a TWIDO TWDLCAA24DRF, and the software I am using is twidosoft. Please help me in solving the problem.
 
Another option would be to upgrade to Twidosuite, which is available as a free download from telemecanique.com.

In configuration set functionality is automatic and this will make sure your PLC has the correct firmware..
 
Last edited:

Similar Topics

HI everyone, i am new to Siemens plc programming and i am in need of some help. yesterday we had an S7-1200 CPU 1214C fail to turn on an output to...
Replies
12
Views
489
I have an old Sentry Palletizer (S/O Number 3007 / Serial Number 1172) that has lost its program as the backup battery died years ago. I can...
Replies
0
Views
161
HOW to communicate with OPTIX and Mitsubishi's Q Series PLC?? PLEASE HELP ME
Replies
0
Views
98
I have a network with 4 PLCs PLC1 is controllogix and PLCs 2-4 are compactlogix and they all need to communicate. The current way I have this...
Replies
8
Views
312
So to start off: I have no experience with PLC's, but I'm good at figuring stuff out, but I need some help to know if my PLC is just dead in the...
Replies
2
Views
148
Back
Top Bottom