BTL_Man Member B Join Date Nov 2007 Location N.C. Posts 3 Mar 3, 2008 #1 Power Flex drive outputting wrong speed to user's plc.... HIM is reading correct but 4-20 ouput is wrong.
Power Flex drive outputting wrong speed to user's plc.... HIM is reading correct but 4-20 ouput is wrong.
DickDV Member D Join Date May 2002 Location Kalamazoo MI Posts 2,324 Mar 3, 2008 #2 The analog output usually can be scaled in the software. 20ma usually is the motor nameplate FLA but, on some drives, it is the drive current limit setting. Better check out which it is.
The analog output usually can be scaled in the software. 20ma usually is the motor nameplate FLA but, on some drives, it is the drive current limit setting. Better check out which it is.