I met the issue on the configuration of SM-Devicenet to 1747-SDN (c. I have only 1 drive (Unidrive SP with devicenet) that is connected to the network.
The problem is that the 1747-SDN always shows error code 79 and flashing red on Module status (net channel indicator is "Off"
When I tried to unplug the terminal at SM-Devicenet side, the 1747-SDN show code 01 --> 75 --> 63 --> 78 and Flashing red @ Module and Flashing green @ Net channel.
I've checked the configuration both side and the results are below;
1747 - SDN (on RSNetworx)
- Address : 01
- Speed: 500k
SM-Devicenet
- Address : 63
- Speed : 500k ( as parameteer 17.04 = 2)
On RSNetworx, the device from SM-Devicenet never exists. Only 1747 scanner appears.
One more thing, I cannot change speed of the SM-Devicenet because whenever I 've changed the drive will trip "SL3.ER" and the Fieldbus diagnostics would show "Configuration error" (parameter 17.06 = -3). This occured even I disconnect the DNET cable at 1747-SDN or changed the speed of 1747-SDN to 125k.
I also tried to restore the default values both side and still the same problem.
I've checked the cable many times and confirmed that it looks OK. Power supply is 23.9 V. CAN H to V- is 4.4 and CAN L to V- is 3.1. and 121 ohms resistors at both ends
Would you please help suggest what I miss or should try more.
Thanks a lot.
PS: On RSlinx I've got the driver diags as attached picture
The problem is that the 1747-SDN always shows error code 79 and flashing red on Module status (net channel indicator is "Off"
When I tried to unplug the terminal at SM-Devicenet side, the 1747-SDN show code 01 --> 75 --> 63 --> 78 and Flashing red @ Module and Flashing green @ Net channel.
I've checked the configuration both side and the results are below;
1747 - SDN (on RSNetworx)
- Address : 01
- Speed: 500k
SM-Devicenet
- Address : 63
- Speed : 500k ( as parameteer 17.04 = 2)
On RSNetworx, the device from SM-Devicenet never exists. Only 1747 scanner appears.
One more thing, I cannot change speed of the SM-Devicenet because whenever I 've changed the drive will trip "SL3.ER" and the Fieldbus diagnostics would show "Configuration error" (parameter 17.06 = -3). This occured even I disconnect the DNET cable at 1747-SDN or changed the speed of 1747-SDN to 125k.
I also tried to restore the default values both side and still the same problem.
I've checked the cable many times and confirmed that it looks OK. Power supply is 23.9 V. CAN H to V- is 4.4 and CAN L to V- is 3.1. and 121 ohms resistors at both ends
Would you please help suggest what I miss or should try more.
Thanks a lot.
PS: On RSlinx I've got the driver diags as attached picture