Hi all,
I am using altivar31 VFD. Through PLC I am giving a signal to L1 of the VFD for controlling the speed of the motor. Now I want a fault indicator. So that I can see it on the panel board. I have studied the manual. In the manual it is mentioned that use the relays. Now how to use these relays. And tell me if there is any other way beside using relays. Any comments will be appreciated.

Thanks
 
The Altivar has two output relays, RA with normally open and normally closed contacts and RB with a normally open contact. Both relays are programmable with respect to what triggers their activation; a fault, a reference speed attained, brake control, etc.

Here is a link to the programming manual: http://www.alamedaelectric.com/Modicon Documents/AC Drive ATV31 Prog Manual.pdf

see page 32 specifically to program the relay outputs

The only other way I imagine to communicate with the Altivar would be some kind of field bus option; profibus, devicenet, etc. I suggest you contact your Telemecanique rep for more information.
 
Hi all,
First of all thanx for the suggessions. But one thing more that I want to ask. should I power these relays or not. Or these relays works as an output. Out of R1A, R1B and R1C how can I connect an indicator light. Because there is nothing in the manual. R1A normally Open, R1B Normally closed and R1C is the common.
 
The relay will energise during fault connecting the R1C to R1A.
If the lamp is 24v DC then connect +24v to R1C, connect another wire from R1A to one terminal of the lamp. COnnect the other terminal of the lamp to 0V.

There should be a drawing to illustrate this in the manual...
 

Similar Topics

Hello, I was having problems finding the correct registers to read some of the registers on a Altivar 630 VFD. I would like to read the following...
Replies
20
Views
9,245
Good Afternoon Guys, I am learning/using Unity Pro S. It is very new to me as most of my experience is with Automation Direct and Allen Bradley...
Replies
1
Views
2,514
I'm trying to configure Altivar 312 VFDs, but my safety circuit drops 3-phase input and currently that also causes the logic/communications to go...
Replies
4
Views
2,518
I am looking at a project where we would be using ControlLogix PLCs and have a Square D MCC.(For financial reasons haha) The VFDs will have...
Replies
14
Views
12,553
Hope to get some input and suggestions from anyone who has had a similar project. Need to control (very low level) 7 different Altivar 61...
Replies
5
Views
3,303
Back
Top Bottom