I have a very remote motor that I need to control and plan on doing it via RIO and a 20-COMM module. I know that you can have local DIs for drive control on a PF70, but can I configure a local DI and then read the status (likely via BTR) in the PLC with no real control to the drive? I want to bring in a zero speed switch to the drive and read its status. Would keep me from having to run another conduit and wire.

I'm thinking maybe assign an input as 'not used', but if I do so, does the status still toggle?

I guess another hokey method is to assign it as accel2 and just set both accels the same.
 
Last edited:
I have done this exact thing using DeviceNet and 20-Comm-D with 1336 Plus II, PF70, and PF700. I set one of the datalinks to the parameter for the digital inputs (param 216). Set the parameter (param 361-366) for the digital in you're using to "Not Used". The PLC will see the input while the drive ignores it.
 
gmferg said:
I have done this exact thing using DeviceNet and 20-Comm-D with 1336 Plus II, PF70, and PF700. I set one of the datalinks to the parameter for the digital inputs (param 216). Set the parameter (param 361-366) for the digital in you're using to "Not Used". The PLC will see the input while the drive ignores it.

Great! That's exactly what I was thinking but wasn't sure that "Not Used" still showed up in 216. I knew Accel2 would.

Thanks for confirming!!
 

Similar Topics

hello everyone! Good Day! there's a possible way to bypass or crack the password when uploading the Screens on (HMI)Proface, GP PRO PB3?? I...
Replies
1
Views
2,614
Hello All, I need the ability to remotely reboot a Red Lion CR3000 HMI. Due to some graphics issues when the database is updated the HMI must be...
Replies
4
Views
219
Hello The plant is running and there is no shutdown nowadays therefore I can add 1734- AENTR and its card while PLC is in Run? I do not wanna...
Replies
8
Views
347
Folks, I have a client with an old ABB Advant / MOD300 system (v14.4). Around y2k I installed the ABB Industrial IT MOD300 OPC Server 1.1/2...
Replies
1
Views
178
Hi all so i have a robot project im working on were i need to set the layers. using the hmi screen i would like to use the numeric data display to...
Replies
11
Views
823
Back
Top Bottom