Panel View C200 (Component)

Maxbrad

Member
Join Date
Jul 2007
Location
Santiago
Posts
10
Hi!
I have tried to stablish communication between my laptop and Panel View C200 (the samallest PV component)via Internet Explorer 7 with its USB cable attached.
Driver has been stalled sucesfully and laptpop reconognize the new device as User manual says; I follow up user manual procedure writing PVc200 IP address but Internet Explorer 7 cannot find it. Any idea about?
 
Last edited:
The PanelView Component USB driver behaves like an Ethernet driver; the Emulator Adapter generally assigns your computer the address 169.254.253.15, and the PanelView Component is always 169.254.254.2.

Of course, that's in the User Manual.

Check your popup blocker settings and make sure you allow popups for the PVc address.

Does the PVc show its IP address ?
 
You might have to change the Alternate Configuration in your Network setup if you and your Panelview aren't on the same Subnet.
 
PVc200 IP shown is 169.254.254.2. I this is I use on the Internet Explorer 7 browser, after a many seconds time out error appears becouse address can not be found.
 
rootboy said:
You might have to change the Alternate Configuration in your Network setup if you and your Panelview aren't on the same Subnet.

This is the message Internet Explorer shows:
Gateway Timeout

The following error occurred:
Code:
 A gateway timeout occurred. The server is unreachable. Retry the request

[/b]
 
Hi Guys:
The problem is the system network permission. We checked it with a external computer without problems. I talk with system administrator to solve it.
Thanks to all
 

Similar Topics

We have boiler control system runs on A-B PLC. The interface is A-B Panel View Plus 7, mounted on the local control panel very near the boiler...
Replies
8
Views
206
Can I connect two A-B Panel View 7 to a A-B PLC. Same graphics etc. One on the local control panel and the other Panel View 7 in a remote control...
Replies
2
Views
71
I have a German programed ME program. I want to know what tag in the PLC a latched button turns on. However when I open up the tag properties I...
Replies
14
Views
245
Am asking if we can upgrade sd ram and cf card of panel view plus ab by a normal sd ram and cf card but Allen Bradley to save cost because in ab...
Replies
9
Views
315
I can't seem to get the Panel View Plus 7 standard edition to downgrade to V_11, when I check the AB downloads and compatibility websites for this...
Replies
1
Views
154
Back
Top Bottom