Trying to Load FactoryTalk View ME Program V_11 to Panel View with FactoryTalk View ME V_13

Join Date
Mar 2024
Location
Oregon
Posts
1
I can't seem to get the Panel View Plus 7 standard edition to downgrade to V_11, when I check the AB downloads and compatibility websites for this current series D there is only two different version at this time both V_13. If that is the case that this PVP7 will not be able to receive a lower version firmware then 13, how would I got about getting the mer. file that is currently for Factory Talk View ME V_11 to become V_13 so it can become compatible with my PVP7?
 
The most recent series likely do not support older firmware. Fortunately unlike with Studio/Logix 5000, the PVP line do not require an exact major firmware match. A panel can generally run a file created in any lower version.

In other words, a panel with v13 firmware should run a v11 .mer file just fine

The reverse is not true, ofc, you couldn't run a v13 file on a v11 panel for example, but that's not relevant here.
 

Similar Topics

Hello! When trying to load the hardware configuration I get error 0050-133 2 2458, check the diagnostic buffer. When checking the buffer, it says...
Replies
4
Views
186
Hi, New to the forum. I have an old machine I am working on that is using aA172SHCPUN. I want to capture the program in case I need to reload...
Replies
22
Views
2,064
Hi guys! I'm trying to download a project to the controller, who already has an aplication running protected by a blank password. The option to...
Replies
3
Views
2,909
Trying to upload the PLC program from SLC 5/04 Using RS232 DB9 cable... already tried with Allen Bradley USB 1747-CP3 1756-CP3 cable... still...
Replies
9
Views
2,296
Good Morning , I received a used 1756-L62 / A CPU , from a vendor that was using it for a trainer. I tried to download a program that is...
Replies
4
Views
1,477
Back
Top Bottom