MPI address of CPU

harrydeharry

Member
Join Date
May 2008
Location
Delhi
Posts
237
01.Is there any mathode to change the MPI address of the 318 cpu.]
02.If new CPU connected what address it will be bydefault or will ask for the same as i never used or configure new cpu
Thanks in advance
 
harrydeharry said:
01.Is there any mathode to change the MPI address of the 318 cpu.]





02.If new CPU connected what address it will be bydefault or will ask for the same as i never used or configure new cpu
Thanks in advance

Go to the hardware config. of your project and double clink on the slot with the CPU, this is slot 2. Go to the properties button next to the MPI network


It defaults to address 2
 
JRW said:
Go to the hardware config. of your project and double clink on the slot with the CPU, this is slot 2. Go to the properties button next to the MPI network


It defaults to address 2
Can we change the address ?
How ?
 
JRW has just explained that to you.
Go to the Hardware (HW Config) in Simatic Manager, right click on CPU -> Object Properties, then button Properties on tab "General" under MPI and you can choose address from drop down list (max 31).
After that, save and compile your Hardware configuration.

Regards,

Pandiani
 
Pandiani,

the max MPI address is not 31, it's 126, but you can choose to limit it to 31. This has to do with communication load on the MPI network.

Kind regards,
 
AFter you've saved the hardware configuration with the new MPI address (not 2) you have to download it to the PLC through its MPI port. Connect the PC to the PLC's MPI port and click the download button in the hardware configuration. It should pop up a window that says something about the connected node being node 2. go ahead select the MPI=2 processor and download. AFter the download the plc processor should now have the new address.
 

Similar Topics

Hello all, Please help me to the way to read the MPI addresses using (step7 lite) program for a PLC (S7-300)and HMI panel connected to it. I know...
Replies
0
Views
1,698
When downloading, I don't understand what this whole business of setting MPI addressing entails. I dig that the station (this computer) and the...
Replies
27
Views
21,380
Hello, Does anyone know how to change the MPI Address on a Siemens TP270 Operator Panel? We are currently in the process of upgrading a...
Replies
5
Views
4,769
Hi I Have new CU320 Module (6sl3040-0MA00-0AA01) for sinamis G150. i want to download Backup config. of old CU320 to new Module with PC Adapter...
Replies
1
Views
527
I have a customer that wants us to use a S7-400 PLC. I don't get into Siemens too often (unless I have to). This machine doesn't do much and...
Replies
15
Views
4,975
Back
Top Bottom