Hi guys,
I'm doing some current consumption for a panel, hope to get some advice from you guys here.
My control panel will be supplying 24V DC to 60 field instruments at 1 Amp each. So total 24V DC for field is 60 Amp & panel about 5 Amp. Total is 65Amp.
Thus, I'll be using 4 units of 1606-XL480E (giving 18Amps/unit) & 1 unit 1606-XL480E for backup. Each 1606-XL480E will be working with a 1606-XLRED20-30 for N + 1 redundancy function. Each 240V AC for 1606-XL480E input is 5Amp, total is 25 Amps. Additional 5 Amps for other panel components.
1) Total is 30 Amps (is my calculation correct)?.
I've another 13 Amp, 3 pin socket in the panel for notebook use. Notebook consumption only 1.5Amp.
2) So my request for the single phase 240V AC incoming to the panel shall be 30+1.5Amps or 43 Amps?
I'm doing some current consumption for a panel, hope to get some advice from you guys here.
My control panel will be supplying 24V DC to 60 field instruments at 1 Amp each. So total 24V DC for field is 60 Amp & panel about 5 Amp. Total is 65Amp.
Thus, I'll be using 4 units of 1606-XL480E (giving 18Amps/unit) & 1 unit 1606-XL480E for backup. Each 1606-XL480E will be working with a 1606-XLRED20-30 for N + 1 redundancy function. Each 240V AC for 1606-XL480E input is 5Amp, total is 25 Amps. Additional 5 Amps for other panel components.
1) Total is 30 Amps (is my calculation correct)?.
I've another 13 Amp, 3 pin socket in the panel for notebook use. Notebook consumption only 1.5Amp.
2) So my request for the single phase 240V AC incoming to the panel shall be 30+1.5Amps or 43 Amps?